Posted on May 10, 2009
Answered by a Fixya Expert

Trustworthy Expert Solutions

At Fixya.com, our trusted experts are meticulously vetted and possess extensive experience in their respective fields. Backed by a community of knowledgeable professionals, our platform ensures that the solutions provided are thoroughly researched and validated.

View Our Top Experts

Ac Problems Im in FL 93F im hooked up to 110 /30 A and i have the AC running the entire day. The Breaker trips several times a day when the compressor kicks in. If i reset it, the entire inside of the coach is flickering and often the Breaker trips again. It a a 2009 Coachmen Prism so the AC is new, it is a 13.5 BTU Dometic Duotherm Roof Unit. The Breaker box is getting hot too.

1 Answer

Dan Webster

Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

  • Dometic Master 8,221 Answers
  • Posted on May 10, 2009
Dan Webster
Dometic Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Joined: Dec 14, 2008
Answers
8221
Questions
5
Helped
2381016
Points
25840

You must have too many things running on that circuit. Check your connection to the power box.Loose connection on the receptacle can cause the breaker to trip or too many things running on the same circuit. If the breaker is old it might need to be replaced.

If you need further help, reach me via phone at https://www.6ya.com/expert/dan_73bbd84fe1d95b61

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
2answers

Coleman Parkpac AC unit tripping GFI breaker

Because they are garbage. They are to sensitive for the actual start up of an air conditioner. Take the gfi breaker out, when day of inspection put it in. Take it out when inspector leaves.
0helpful
1answer

Rittal enclosure ac compressor no start but ac display A02 coming then power breaker trip how to troubleshooting

the failure to run the compressor then tripping a circuit breaker indicates either a failed start/run capacitor or a seized compressor motor
for this error ,it would be best if you got in an ac technician to properly diagnose the fault and get a quote
0helpful
1answer

AC trips circuit breaker not long after a recent power outage.

Sounds like your compressor is shorted to ground. If you are able, unhook compressor, wrap wires and restart. If breaker doesn't trip than u know.

If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79

0helpful
1answer

Compressor runs for only a moment the circuit breaker trips

Lights dim, moaning from AC, just before it trips breaker? Have you checked incoming voltage? What type of plug are you hooked up to, 30, or 50 amp?
0helpful
1answer

AC runs for 5 minutes and then circuit breaker

What else do you have running on hydro while AC is running? Such as coffee maker, microwave, water heater, fridge. That 30 amp breaker is your main breaker I assume, or breaker on pole your plugged in to. Keep in mind your AC will normally draw approx. 15-17+ amps momentarily when compressor kicks in to cool, then drop back to 12-15 amps when running normal. If your AC is drawing too much current, then you would only normally trip 20 amp breaker for AC in your panel. Try switching other appliances to gas operation while running AC, such as water heater, and fridge. Make sure incoming voltage is up to specs as well . (115-120 volts)
If water heater takes 5-8 amps, and fridge takes same when they are calling for power, you'll be close or over the 20amp mark when you consider your on board converter etc. as well. That only leaves approx 10 amps for AC that requires approx 15 amps to run, and up to 20amps when compressor kicks in. If you switch all those other items over to propane, and it still happens, then a current draw test should be done on AC unit to see if perhaps a capacitor is faulty, or possible compressor faulty.
1helpful
2answers

My unit was working fine until 3 days ago when the breaker tripped, I reset the breaker and worked fine for a day then tripped again when it tripped both the ac breaker andthe main in the trailer as well...

High amp draw can be caused by a few different things, so first check that incoming voltage to trailer is sufficient. (115 volts) Not unusual for some parks to install more hydro hook-ups on a feed line, and when all are up and running, your incoming voltage could be decreased. If your o.k. that way, then I'd start looking at the compressor circuit of your ac, in particular, the compressor start-up capacitor. The capacitor basically stores electricity and boosts it to higher voltage for compressor and fan start-ups to reduce current draw that will trip the breaker. Please have a knowledgeable electrician, or RV tech check this for you, as a capacitor can give a real good high voltage (possible fatal) shock, even when power is off to unit. I also suspect that the start relay has shorted (welded) itself due to high amp draw situation, and that is reason it comes on by itself.
0helpful
1answer

AC Runs for about 10 minute then trips breaker

is your breaker is ok or lose concation is good.if this both is good than cheek his overload.
1helpful
1answer

Hitachi RAS09UH randomly pops 15A circuit breaker

Two things that you could check: 1) If you have access to an ampmeter, determine if the unit is drawing over over 14 or 15 amps, 2) replace the suspect circuit breaker in case it is beginning to go bad. Breakers only trip for overcurrent conditions or failure of the breaker itself. If it is pulling close to 15 amps, then it could heat up over time and trip.
0helpful
1answer

The unit runs fine for a couple of days then trips. some time it will trip twice a day

The compressor may be old or the starting capacitor is weak. Could be bad connection on the AC supply line or pitted contacts on the run relay. Check all AC wiring supply connections even in the house electrical panel for tightness, Replace the starting capacitor first.
If it still has a problem install a hard start capacitor kit. Could even be a bad breaker - breaking out on a lower current draw.
1helpful
1answer

Air conditioner will trip breaker when trying to cycle back on

The compressor motor , once warm is grounding out due to wear and is going bad.Have the compressor replace while it is still clean is cheeper and easier that doing it after a burn out,which  will eventually happen,if the compressor is tripping the brreaker as I suspect..
Not finding what you are looking for?

431 views

Ask a Question

Usually answered in minutes!

Top Dometic Heating & Cooling Experts

ZJ Limited
ZJ Limited

Level 3 Expert

17989 Answers

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers

Mike Cairns
Mike Cairns

Level 3 Expert

3054 Answers

Are you a Dometic Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...