UPS displays site wiring fault alarm and input voltage/freq out of range even though the wiring and input/output is ok
Hi Viqtah, (<------ Clever!!)
If you hit the ESC key and get to the main menu there is a Setup submenu. In there you can change the line voltage values coming into the UPS. Sometimes a previous owner will change those values and cause the UPS to fault when properly connected. NOTE: A CERTIFIED ELECTRICIAN SHOULD VERIFY ALL CONNECTIONS ENSURE PROPER PHASE ROTATION.
Reply or call if you have any more questions -- 800.260.2259
SOURCE: problem with SmartUPS SU5000I
Before trying to replace an IC, make sure that the battery is capable of holding a charge. If there is more than 1 battery, check all. If it (they) are bad, it will probably be less expensive to replace the unit.
SOURCE: no output
Check the DC fuses in the ups. One of those fuses must have blown, replace with one of the same rating...............sodeep
SOURCE: "On Battery" Alarm Sounds when Power Available.
if this comes sometimes and goes, this means that the power to ups is sometimes deviating from the specific ups input range, hence the ups is rejecting it. mesure the input voltagesand frequency with a multimeter and check whether they match the specified ones in the ups manual. aslo with some ups there are switches that you use to set the input voltages or number of phases in the ups input. check the manual to see whetther your ups has such.
SOURCE: When I turn UPS it starts to make a squealing
yes one side of the mosfet is faulty can be found by multimeter desolder and replace it