Kohler 12 kW Emergency Power System - 12RES-L Logo
mike Whalen Posted on Sep 18, 2013
Answered by a Fixya Expert
Trustworthy Expert Solutions
View Our Top Experts
8.5 kohler generator battery dies often - Kohler 12 kW Emergency Power System - 12RES-L
Renee F
Level 2:
Prodigy:
An expert who has answered 500 questions.
  • Kohler Expert 573 Answers
  • Posted on Nov 16, 2013
Renee F
Kohler Expert
Level 2:
Prodigy:
Answers
573
Questions
0
Helped
247942
Points
680
Check the battery charger whether an external one is installed or the optional one ion the transfer switch. Measure the voltage on the battery it should be at least 13.8V if it is only 12V then the charger is suspect. Also if it is an external charger plugged into a receptacle make sure that the 120V receptacle is hot (GFI's) tend to trip in a storm
1 Related Answer
Anonymous
  • 169 Answers
  • Posted on Dec 03, 2008
SOURCE: kohler 12kw generator starts but shuts down after 3sec
Your gas pressure is too low and you may not have a large enough supply pipe. You need at least 10 inches of water column with the engine running to operate an LP vapor fueled engine. Because the engine is starving for fuel, its governor opens the throttle to WOT (so it goes to high revs) but there isn't any fuel to make horsepower with so the output voltage falls and the undervoltage alarm trips.
Carl
Kohler House Generator powers up when our electricity goes out but then powers right back down?
That is an engine running issue, not a battery issue. :>D The first thing to check would be fuel supply. Can you start up manually and keep it running. If you can, it is the contactor that senses your loss of mains power and switches the generator on. It is not maintaining the connection, or is is misdiagnosing the power from the generator as power from the mains.
1helpful
12 RES - Control Panel Dead With New Battery
If it won't start in manual, you have a short and/or a bad control board. Make sure battery polarity is correct, did you disconnect battery charger before removing old battery? If not charger can push DC volts over 20V and can damage control board.
14kw kohler propane generator-sometimes does not start, put battery jumper on and it starts. Battery is new, but had the same problem with the old battery.
The battery charger is defective, as you can start it by jumping it off means it is just a low battery. without it running measure battery voltage, it should be around 12V then plug the charger back in, it should climb to around 13.8B with a good battery. If not have the float charger checked.
Kohler generator wont stay on
Check the oil pressure switch, and oil level first. Then check rotor brushes and rotor slip rings may need polishing. If the problem is still there check stator and rotor windings
My gen starts and runs for 1 min or so then dies restarts then dies again and again. if i start it under load ( turn on air con) it will run for 10 min then die allen
Is there a fault?? All UL listed generators including Kohler are required to lockout on a fault on shut down. This really sounds like a problem with your 2-wire auto start connection between your automatic transfer switch and genset. RDT model automatic transfer switch it is the 2 middle wires on the green connector and terminals 3&4 in the generator. close to run and open to shut down. Any open at any time will cause the unit to shut down. The 12 will shut down instantly upon an open because your 5 minute cool down is built into the transfer switch.
Kohler generator drains battery while running and then shuts down with error code oc
The rpm sensing in the control module is missing or bad.
Answer these questions for more details:
  1. Does your generator output normal voltage?
  2. Is the starter turning after the Gen is running?
  3. Is the charging of the battery connected?
4helpful
3answers
Kohler small engine problem
1989 Kohler 20 backfires through the exhaust. What are the possible causes?
Top Kohler Electrical Supplies Experts
john h
ADMIN Andrew
ADMIN Andrew