Electrical Supplies Logo
Posted on Apr 12, 2009
Answered by a Fixya Expert
Trustworthy Expert Solutions
View Our Top Experts
Guardian generac 10kw model 5502 does not output correct voltage
The generac manual does not indicate how to adjust the 10kw model 5502 voltage. This model uses the small V-twin engine but is connected to the same generator as the 8kw model. To adjust the 8kw model the manual says to adjust the engine governor and the 12 to 20kw models have voltage adjustment potentiometer to adjust voltage. There is no mention on how to adjust the voltage for the 10kw model.
I'm currently getting 105v line to neutral and 210v line to line. Any help would be appreciated.
  • dschantz26 Apr 13, 2009
    the instructions say to NOT apply load to the generator until the voltage is in the recommended range. in this case (ie the 10kW set) the line to line range is 220 to 230 volts. i'm getting only 210 volts. How do you manually change the motor speed? and what is the best device or instrument to check the frequency? why would adding load INCREASE the voltage? i'm reluctant to add load which may harm my electronic devices and motors with under voltages.
    I put a small load of a few lights on the generator and low and behold
    the voltage shot up into the normal range. I continued to add load
    including two freezers, a refrigerator, TV, two pumps and three rooms
    of lights. The voltage stayed in range and I am now satisfied that the
    generator is running properly. It appears that the electronic voltage
    regulator needs to sense a load before it actuates the governor. This
    is a nice feature, in that the weekly exercise will run at a lower RPM
    and save a few gallons of LP gas.
    Thanks for your help.
    Dan
Kenneth
Level 2:
New Friend:
  • Expert 50 Answers
  • Posted on Apr 13, 2009
 Kenneth
Expert
Level 2:
New Friend:
Answers
50
Questions
0
Helped
50159
Points
127
The instructions says the voltage regulator is automatic/digital. when you check the voltage is there any load on the generator? if applying load to the generator doesn't help, you can manually change the motor speed where the governor connects to the carborator, but it may change the frequency, but the regulator may fix it
  •  Kenneth
    Kenneth Apr 13, 2009
    applying load will increase the excitation current (its how the generator knows to start making electricity) anyways, i usually use a shop light for my load, you can't hurt them with low voltage. the adjustments for the motor speed will be mechanical (prob. a screw or linkage) i would call customer service if all this fails, they actually help pretty good
Generac 0058711, 10KW Generator. How to reflash home standby 10kW Generac generator model number 0058711 please.
That is a full home back-up unit. You need dealer support. Contact them direct. There is nothing online about re-flashing.
Support For Your 0058711
Generac Power Systems https://www.generac.com > product-support-details
File Type Manual (PDF) Item Number Langu... Emissions Warranty Statement WARRANTY STATEMENT EMSN E P3 0J3335 EN Exploded View (Control Panel) EV CONTROL PANEL ? HSB 0J3707 EN Exploded View (Enclosure) EV ENCLOSURE HSB 2011 0J4730 EN View 29 more rows
13w guardian generac generator 054960 doesn't charge battery
Check "F1" fuse.
If fuse is good, check voltage at battery.
With either utility power present or generating running, the voltage at the battery should be >13VDC. Any reading less than 12.7VDC is battery voltage and indicates a failed charging circuit.
We have a generac 10kw pad mounted generator and the battery has blew up two times now, what would cause this to happen? The entrie battery blows up into pieces. The generator has proper...
The battery is overcharging either by the external charger or by the engine alternator. This is causing the battery to "boil" realeasing hrdrogen gas. One spark or high current demand from cranking can cause this. Have it checked by a pro
2helpful
Battery does not stay charged on my 20kw generac generator
WAS A 110 VOLT CIRCUIT RAN TO IT FROM THE NORMAL UTILITY POWER OF HOME OR BUILDING IT FEEDS?
NORMALLY THIS IS DONE IN A SEPERATE CONDUIT FOR CONTROL WIRES.AND THE FEEDERS ARE IN ANOTHER CONDUIT.
WITH A DIGITAL TEST METER,CHECK FOR 120 VOLTS AT THE BATTERY CHARGER IN THE GENERATOR CABINET.USUALLY THERE IS A RECEPTICAL TO PLUG THE CHARGER INTO.
IF VOLTAGE IS PRESENT AT THE BATTERY CHARGER AND INDICATOR LIGHTS ARE ON, CHANGE METER TO DC AND CHECK FOR 13.8 VOLTS OUTPUT FROM THE BATTERY CHARGER.IF YOU HAVE OUTPUT VOLTAGE TO THE BATTERY,AND IT IS DEAD,CHANGE THE BATTERY..
HOPE THIS HELPS YOU,BEST OF LUCK.....
Hi: I have a model 0052411 Guardian generator that is putting out 170 volts. Anyone have any idea what has caused this to happen. It has fried any transforms that are in the house. Generac is not much...
Check the automatic voltage regulator .Or if you have a bad neutral connection one leg will be very high and one leg low causing damage to sensitive equiptment.
2answers
I have a 10 KW Generac Guardian Stand By withe a prwired EZ transfer swithc. Everything works except the 12 volts battery charger. What could be the problem. Only have three weeks innstalled.
Your generator is equipped with a battery trickle
charger that is active when your unit is set up for
automatic operation. The trickle charger is
designed to help extend the life of your battery by
maintaining the battery when the unit is
not running.
you will need to review which circuit bord controls this and have that board replaced or serviced some of these gen heads have this built in and it will be the rectifier in the gen it self it will be a black 1x1x3/8 inch with a mounting hole in the center and 4 lug post for the wires replace this and your issue should be solved but consult your dealer for witch unit you have as to a control board external or the built in rectifier hope this helps.
No electrical output
It is possible that your voltage regulator is shot but before purchasing the volt regulator try flashing the fields first and make sure the brushes and rings are clean.
Top Guardian Electrical Supplies Experts
ADMIN Andrew
ADMIN Andrew
Kardoc
CJ Rock
CJ Rock
Are you a Guardian Electrical Supply Expert? Answer questions, earn points and help others