Amana PTH153B50AM Air Conditioner Logo
A
Anonymous Posted on Apr 01, 2013
What does br mean?
My air/heat unit flashes br and then shuts off,
Hunterfan 44260 blowing cold air and flashing 4 blower keeps turning on and its not flowing a normal cycle, they are short turning off and then on again
The "4" only indicates which program is currently running. This thermostat does not display furnace error codes.
In a heating system that uses hot wire ignition for natural gas or propane, this behavior may indicate the furnace failed to detect a flame when the cycle starts. You may get warm air briefly, but because the flame detector isn't working, the system shuts down. After a while, it purges any gas and tries again. The controller board in the furnace may have an indicator light that flashes an error code - look for a label on the access panel that describes what it means.
One common cause of this problem is a buildup of contaminants on the flame sense rod (often the same rod that heats red-hot to ignite the gas). Turn off the power to the furnace, wait for it to cool, then inspect the rod. If it has a whitish film on it, clean that off with Scotch-Brite (TM) or similar product (don't use sandpaper). The flame sensor works by measuring a tiny electrical current through the flame. A buildup of combustion products on the sensor blocks this current.
Warning: if you are not absolutely certain about which part is what in the furnace, don;t take any chances, call in a professional. This is a critical gas safety component.
My portable unit just flash's red when turned on
http://www.ehomeservices.com.sg/articles/how-to-solve-air-conditioner-light-blinking-problem.html
If you see the red flashing light during regular operation, this usually means that the outdoor unit was shut off due to a problem and is currently "locked out" from normal operation. When you see the red flashing light, it is usually in a diagnostic feature to alert the HVAC repair technician to what the problem is.
https://www.onehourheatandair.com/bay-area/about-us/blog/2016/may/what-does-a-thermostat-red-blinking-light-mean-/
2answers
Heater runs for 2-3 minutes then quits
Either the unit is over heating and being thermally shut down or the temp shutdown switch is shutting down prematurely.
Burnt wire smell Board Flashing Br
The unit was running when we came in. No Storms in the area. it was blowing hot air, but was still on the cool setting. There was a burnt wire smell coming from the unit. And the diag. code was Br. I found this odd since it still had power.
Flashing light the at says e6
Usually Indoor Unit Anti-freezing protection (Cooling
Mode) or Over-heating Protection (Heating Mode)
for Evaporator
A) Indoor room
temperature too low
under cooling mode,
Too high under
heating mode
B) Indoor unit filter or
evaporator too dirty
C) Indoor unit fan motor
blocked
D) Insufficient refrigerant
under cooling mode
E) Indoor unit evaporator
sensor wrong
connection or failure
Is a RUUD UBHC-14J11NFH a heat pump?
Ruud UBHC-SERIES is a HEAT PUMP AIR HANDLER
AND FAN COIL UNIT
Compressor and condenser not included
Spec sheet go here
http://yaunco.com/pdfs/rheem/ubhc_specs.pdf
I have an AC unit with the model # PDH12K3SD-C the unit stops working and flashes an error cod = "06" anyone know what the error code means?
According to the Owner's Manual if the Error Code flashes "06" the O.D. coil Temperature > 175 Deg
F for 2 consecutive minutes. (Heat Pump models only).
The action taken by the unit is Alternate flash set point and error code. Shut unit down for 5 minutes, then try again 2 times, if fails the 3rd time, then shut down unit.:
All of this is can caused by several things:
• Dirty filters
• Dirty coil
• Fan motor failure
• Restricted air flow
• Improper refrigerant charge
• Restriction in refrigerant circuit
The dirty filters, dirty coil and restricted air flow you can troubleshoot and solve yourself. The reaming ones should be handled by a an authorized service technician.
Here's a link to your Owners Manual, that you can download and print for future reference.
http://www.ajmadison.com/ajmadison/itemdocs/92008705_9-07_PTAC_IO_manual.pdf
Hope this helped to to troubleshoot and solve the problem . Please let me know. Thanks.
2helpful
2answers
Its 15 degrees outside and my amana unit is off. every so often it kicks on by itself and runs for about 10 seconds then shuts off again. while it is running the control panel flashes FP, what is it trying...
I was wondering the same thing about our unit until I found the specs online and read that it has freeze protection. When the temp goes below 40 degrees, the fan comes on to prevent damage to the unit.
Coleman evcon dgat090bdd. New ignitor won't heat up.
Looks like 4 flashes might be high limit fault on this furnace. (I don't have a manual for this furnace, just searched online for the code meaning) Is the unit running flame at all? Is the unit running flame for a while then shutting flame off before desired temp is reached? Does the main air fan turn on to circulate air through your diffusers? Does it feel like the unit has much air flow out of the diffusers if the fan is running? Is your air filter clean? If it is infact your high limit switch, it is usually caused by not having enough airflow through the furnace and overheating occurs.
Hope this helped, let me know if I can assist you further :)
Arcoair central heat /air conditioning unit
The blower motor kicks on when there has been a 24 volt control failure.
This usually means that a limit switch has tripped.
Most likely that would be a high temp limit switch or a rollout switch.
First, make sure the filters are clean. and the evap coil is clean. If eaither are dirty/clogged, it will partially block airflow, causing the furnace to overheat, causing the high temp limit to trip.
A rollout switch typically trips for three reasons.
1 flame rollout into the burner compartment due to poor airflow.
2 overheating af teh metal plate the rollout is mounted to, due to dirty, old, rusted components.
3 a bad limit switch.
If your unit has an LED light, count the flashes and it will hepl popint out the problem.
(locate the wiring diagram/flash code list, and correspond the flash count, with the code.)
First, check filters.