Ground Fault ???
Troubleshooting Ground Fault
Troubleshooting a ground fault circuit interrupt, or GFI,
breaker is pretty straightforward. Troubleshooting the circuit itself can be
quite time-consuming.
The GFI breaker is designed with a test button incorporated
into the breaker itself.
Pushing the test button should trip the breaker.
On GFI-style breakers the neutral wire going into the
house's outlets is connected to the breaker's neutral connector, the white
neutral that comes out of the breaker is connected to the neutral bus in the
panel, isolating the neutral bus from the neutral wire going into the house.
The test button actually shorts the neutral wire feeding the
circuit to the neutral bus in the electrical panel creating a ground fault that
It is considered a ground fault because the neutral bus in
the main electrical panel is actually connected to the ground bus through the
panel's metal casing.
What to do if the test button isn't
tripping the breaker
Push the test button on the GFI breaker.
The breaker should trip.
If the breaker does not trip, then it may be that the
breaker has already tripped and just looks like it's on.
The position of the switch may only move slightly from the
on position towards the off position when tripped.
Push the switch on the GFI breaker all of the way toward
the off position.
It may take some force to get the breaker to reset.
Turn the breaker back to the on position.
When the breaker has been reset properly you should feel
some resistance when pushing the switch back on.
Push the test button again and the breaker should trip.
If the breaker still doesn't trip then you should test for
power at the screw connections inside of the electrical panel.
Remove the screw that holds the dead front covering the
breaker's connections.
Remove the dead
front cover.
Test for power with your voltmeter set on AC volts on the
highest scale.
For a single pole GFI breaker, touch the black lead from the
tester to the silver screw on the GFI breaker and touch the red lead from the
tester to the brass screw on the GFI breaker.
You should see 110 volts on the tester. If voltage is seen
but the test button won't trip the breaker, then the breaker is bad and should
be replaced.
5
Test for power on a two pole breaker by touching the red
voltmeter lead to one of screws with a black or red wire connected to it.
Touch the black lead to the other screw with a
You should read 220 volts or close to it on your
voltmeter.
If you read voltage and the test button won't
trip, the breaker is bad and needs to be replaced.
What to do if the breaker won't reset and keeps tripping
when turned on
6
Unplug everything that is plugged into any of the outlets on
the circuit in question.
Try resetting the breaker again by pushing the switch all
the way to the off position and then turning it back to the on position.
If it won't reset and trips when the breaker's switch hits
the on position, it could be a bad breaker or a problem in the circuit itself.
7
Use your straight-tipped screwdriver to loosen the brass
connection screw or screws on the GFI breaker.
Pull the black hot wire, or wires, out of the breaker's
connectors.
Loosen the silver screw the white wire is connected to and
remove it from the GFI breaker.
8
Push the switch all the way to the off position.
Turn the switch back to the on position.
If the breaker still won't reset, then the problem is the
breaker itself and it should be replaced with a new one of the same size, brand
and model.
If the breaker
resets normally and the test button trips the breaker when pushed, the problem
is in the circuit itself and an electrician should be called to find your
ground fault.
9
Reconnect the black wire, or wires, to the brass screws on
the GFI breaker.
Reconnect the white wire to the silver screw on the GFI
breaker.
10
Replace the dead front cover into the breaker panel.
Install the screw or screws that hold the dead front in
place.
http://www.hilo-electric.com/blank?pageid=63