Goes on for 3 min than shuts off, fault light goes on

2 Related Answers

Anonymous

  • 169 Answers
  • Posted on Dec 03, 2008

SOURCE: kohler 12kw generator starts but shuts down after 3sec

Your gas pressure is too low and you may not have a large enough supply pipe. You need at least 10 inches of water column with the engine running to operate an LP vapor fueled engine. Because the engine is starving for fuel, its governor opens the throttle to WOT (so it goes to high revs) but there isn't any fuel to make horsepower with so the output voltage falls and the undervoltage alarm trips.

Carl

Ad

Anonymous

  • 41 Answers
  • Posted on Sep 06, 2011

SOURCE: I have Kohler 12Res generator,sometimes

If it has a couple hundred hours or more, try cleaning the slips rings on the back of the rotor shaft. They should be very shiny and not black or polished looking.

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1helpful
2answers

Kohler generator 5E run but not well, keep shutting off

http://www.kohlerpower.com/onlinecatalog/pdf/g2058.pdf
Safety shutdowns:
  1. Loss of coolant
  2. High water temperature
  3. Low oil pressure
Likely one of these. If no indicators at a panel check at the connector.
0helpful
2answers

Aux fault on Kohler generator 5ekd says 17.0 fault check engine

More supports or if you consider diesel generator set in furture, please contact [email protected], or visit at: www.dieselgeneratortech.com
1helpful
1answer

Why does my Kohler 7.3 generator start and runs great for about 5 min. then shuts downRestarts fine but shuts down seconds later. Upon removing rad cap, fluid is seen moving upon warm up. How do I...

change the oil to the correct specification first. As the engine runs the heat changes the viscosity and overheats or trips the oil alert switch. If its over 10 years old change the oil alet magnetic switch
0helpful
1answer

My kohler 4ckm21 generator starts great but will run for 8 min. and shut down ?

If it runs that long, you may have a bad oil pressure switch, loose connection, or fuel pump. You didn't indicate whether the time was under laod or not
0helpful
1answer

I have a Kohler 12 RES home standby generator. Once in a while when the power goes out the generator will start and then immediately shut down with no fault codes. When I flip the control in the unit

Check the inlet fuel pressure, on exervise there is no load, when power is out it is loaded and demands more fuel. Also check for bugs blocking gas regulators vents etc
1helpful
1answer

I have Kohler 12Res generator,sometimes it runs fine and sometime it runs for 5 min and then shut down with error code UU (under voltage).I cant find authorized service center in Pakistan.Please help me to...

If it has a couple hundred hours or more, try cleaning the slips rings on the back of the rotor shaft. They should be very shiny and not black or polished looking.
0helpful
1answer

My gen starts and runs for 1 min or so then dies restarts then dies again and again. if i start it under load ( turn on air con) it will run for 10 min then die allen

Is there a fault?? All UL listed generators including Kohler are required to lockout on a fault on shut down. This really sounds like a problem with your 2-wire auto start connection between your automatic transfer switch and genset. RDT model automatic transfer switch it is the 2 middle wires on the green connector and terminals 3&4 in the generator. close to run and open to shut down. Any open at any time will cause the unit to shut down. The 12 will shut down instantly upon an open because your 5 minute cool down is built into the transfer switch.
0helpful
2answers

I have a Kohler 12RES, 12.5kw genset. Less than a

check connections on speedsensor or take down rpms must be a screw or bolt on de fuelpump
Not finding what you are looking for?

90 views

Ask a Question

Usually answered in minutes!

Top Kohler Electrical Supplies Experts

Brad Brown

Level 3 Expert

19187 Answers

john h

Level 3 Expert

29494 Answers

ADMIN Andrew
ADMIN Andrew

Level 3 Expert

66850 Answers

Are you a Kohler Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...