When batteries damaged and one capacitor burnt
SOURCE: Powerware 9120 DC Bus Fault Problem.
there is a 100uf/63v capacitor near the IRF630 fet. You need to replace this in order to fix this error. Along there is also a 2200uf/16v capacitor. It is a good idea to change the both at the same time.
SOURCE: No Power
You should measure AC voltage from the output of the transformer to the bridge rectifier, and after the rectifier you should see a DC voltage (you may also read some "ripple" AC voltage on the DC side as well). Check across each battery to see how many volts DC they are receiving (as they will all be in series connection ie one after the other). Batteries are the usual problem with faulty UPS's. You may have a problem battery or multiple problem batteries and they may need replacing.
SOURCE: Battery Packs for Powerware 9355 UPS
If you battery packs are all at 130volts DC, then all of the packs will have become dead, and the batteries are not recoverable. Your battery DC bus voltage on a Powerware 9355 20 to 40kVA rated UPS is nominal 432 volts DC - 36 batteries in series in each string at 12 volts DC per battery. If batteries go below 10.5 volts DC each, or 378 volts DC bus voltage, no amount of charging will recover these batteries. You should not be recycling the DC battery breaker, unless you felt the battery breaker was faulty. The UPS would have given you an alarm message of either battery breaker Off, Charger Failure, or Low DC Bus Voltage long before the these batteries failed.
The battery test will not proceed if the batteries are dead.
Toll Free: 1 800 356 5737
E-mail: [email protected]