SOURCE: I have a Lennox Pulse

Hi,
That can be a bad relay, but it also can be the high limit has tripped...or went bad...when the high limit thinks that the furnace is too hot the blower will run continuously...
The best way to troubleshoot is to unhook a wire from the high limit and see if the blower stops... if it does then the high limit is bad or needs to be reset...

if it continues to run then the relay is likely welded together...

heatman101

Ad

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

I can't find any batteries in my Lennox Y2018 comfortsense thermostat

Oddly, I can't even find the Y2018 model on the Lennox site nor on the entire internet. I looked at a 7500 comfortsense manual and no where in that manual is a battery mentioned. Some thermostats do indeed contain batteries to preserve settings.

The Lennox home site seems to direct people to Lennox dealers. If the manual for your thermostat does not include a support number other than warranty, you may have to talk to a dealer/installer. Sorry.
Jun 29, 2018 • Cameras
0helpful
1answer

I have a lennox pulse 21 And if i set the thermostat to auto the unit kicks off after a min and the limit switch goes over 200. But if i keep the fan on the unit works fine.

See if you blower speed is set to low speed in the heat mode.
I think what might be happening is the blower is set to low speed in heat and when you switch to automatic, the blower is switched to high speed. You may have to change the blower speed to high in the heat mode. If not you may have an airflow problem such as a Dirty filter, ducts not sized right, dampers on the room outlets closed.
1helpful
1answer

Where to find parts list for Lennox pulse 21 G21Q3-80-2.

Click the link below. It is in PDF format. http://www.hvacpartsshop.com/manuals/G21_Series.pdf
0helpful
2answers

Lennox pulse 21 startup issues .does not engage fan and complete heat cycle every time .

Have seen a rash of faulty blower time delays in lennox equipment. Lennox has a recall on one currently, not sure if your system is effected but it can be bypassed if in fact the problem.

If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79

1helpful
1answer

I have a Lennox Pulse 21 model G21Q4/5-100-3. The blower motor will not turn off even if the thermostat is in the off position. I suspect a stuck relay or control. Any advice?

Hi,
That can be a bad relay, but it also can be the high limit has tripped...or went bad...when the high limit thinks that the furnace is too hot the blower will run continuously...
The best way to troubleshoot is to unhook a wire from the high limit and see if the blower stops... if it does then the high limit is bad or needs to be reset...

if it continues to run then the relay is likely welded together...

heatman101
4helpful
1answer

Lennox pulse 21 furnace - nothing runs on but control board tries

you will need to verify voltage from the board to the inducer. If you have the installtion manual there is a flow chart for the sequence of operation of the furnace.
The basic sequence is:
1. thermostat calls for heat
2. inducer motor starts and runs for a pre-set amount of time
3. the pressure switch closes and allows for ignition trial
4. ignition is proved back to the board allowing the system to operate.

Verify 120VAC to the inducer motor upon call for heat from stat, if you have 120 at the leads that connect to the inducer and it does not start , the motor is faulty. If the inducer starts use a voltmeter across the pressure switch terminals, a voltage reading of 0 VAC will verify contact closure and ignition should occur.

The pulse furnace was under a factory recall due to breaches in the heat exchanger, unfortunately for you, the Lennox Corp. has ended the program that allowed for an allowance / furnace for replacement. To test the heat exchanger a special kit is required from lennox that will verify integrity of the heat exchanger. (If the heat exchanger seal has been comrimised the pressure switch will not prove and the igniton sequence will be interupted and cause the system to go into "lock-out" mode).I know this is probably not what you wanted to hear. Hope this helps, please list as "very helpful" if it did
0helpful
1answer

I have Lennox pulse 21 control module light goes out

If this is a high eff model, check to make sure the intake vent is not plugged.

0helpful
2answers

I have a Lennox Pulse furnace. It's making a

The bearings are bad. You need to replace the motor. Motor cost $75 to $125. Labor is on avg. $150 to $400 with an decent A/C Company . You can try to oil it but its not recommend by Lennox. That furnace at the time they build it was top of the line. Good Luck.
Not finding what you are looking for?

189 views

Ask a Question

Usually answered in minutes!

Top Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

john h

Level 3 Expert

29494 Answers

Brad Brown

Level 3 Expert

19187 Answers

Are you a Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...