Carrier 38CKC060 Air Conditioner Logo
Anonymous Posted on Oct 29, 2011
VERTICAL STAND ALONE CARRIER SPLIT AC UNIT MODEL 42SD7C GIVING Er 03 code on display. may i know this code is for what fault in sysytem.
5 Related Answers
Ken Bledsoe
  • 306 Answers
  • Posted on Dec 11, 2008
SOURCE: Tonnage of my Carrier AC Unit
3 1/2 ton unit the 042 tells me.
Anonymous
  • Posted on Dec 16, 2008
SOURCE: Carrier Thermostat Model TSTATCCPB501 ER code
I gave up and called a local HVAC business. This thermostat is discontinued and a new one will be purchased and installed.
bobotfel
Felizardo Erilla
  • 241 Answers
  • Posted on Jan 08, 2009
SOURCE: not turning on
Hi
Try to reset the unit by disconnecting the power supply for 10sec. and operate the unit. If it wont work replace your Room Air and Coil Thersmistor or test the thersmistor with mulitester. The resistance reading of thermistor is 10 kilo ohms @25deg. C room temp. If it is shorted or open the unit wont operate.
Hope this can help :)
Donni Steen
  • 687 Answers
  • Posted on Mar 30, 2009
SOURCE: carrier split 42G250HF-1(indoor unit
I'm not sure exactly what unit you have and what controls you have installed on the unit. But....there usually is a flash code schematic on the unit. Usually on the inside of the blower compartment cover. This should tell you what is wrong with the unit. It could have a low voltage short somewhere and is loosing the call for cool. So the answer can be a possible yes to your question but without knowing the flash code, it's hard to tell from my point of view. You might end up calling a service professional out to check it.
Anonymous
  • Posted on May 21, 2010
SOURCE: ERROR CODE 5 FLASHES CARRIER SPLIT SYST. AIR COND. 42G250HP-1
5 flashing is ' compressor drive' and check the high pressure, condenser fan motor capacitor for proper running
Xantrex Freedom X won't run refrigerator, and error code 03.
Question edited for clarity. Error is zero-3 not letter oh-3.
There are three models, an your load has exceeded its capacity
E03 AC output overload shutdown Reduce the loads connected to the AC outlet of the unit. Check appliances that have high-surge ratings and disconnect if necessary. NOTE: This could be a logical fault, hard reset and reassess the error condition.
Aug 30, 2021
Xantrex Freedom HF 1800 Inverter/Charger - Fault Code And ...
https://xantrex.com/products/inverters/freedomx/
https://www.google.com/search?q=xantrex+freedom+x+error+code+03
What is the meaning of error p9 in carrier window type inverter?
Error Code Definition: (Unit Size 36K - 42K) = IPM over temperature protection. Carrier AC Indoor Unit Displays Error Code: P9. Error Code Definition: (Unit Size 18K - 24K - 30K) = NA. Error Code Definition: (Unit Size 36K - 42K) = Open Contactor.
https://removeandreplace.com/2017/08/11/carrier-split-system-air-conditioner-error-codes-and-troubleshooting/
https://www.youtube.com/watch?v=M-fLGOYL84Y
H4 error code is shown on AC display what can i do to slove this problem
Full list of Gree Air Conditioner Mini Split Units Fault Codes. When error codes appear on the Gree air conditioner indoor display, this tells the user there is an issue with the Gree AC unit. The error code displayed will inform you of the issue or problem that is occurring with the air conditioner. Knowing what the error code means and its definition will help you to understand and troubleshoot the exact Gree air conditioner part that needs to be fixed, cleaned, repaired, or replaced. You can then clean, fix, or replace the Gree part yourself and save money. See below for all error codes that can occur on Gree Mini Split AC's.
Gree Mini Split Air Conditioner Error Codes - How To Fix
Gree Viero AC Mini Split PDF Owners and Troubleshooting Manual
GREE DUCTLESS AIR CONDITIONING & HEATING SYSTEM INSTALLATION MANUAL
Gree Mini Split Air Conditioner Part Names and Locations
INDOOR AND OUTDOOR UNIT
The Gree Air Conditioning Vireo System has onboard error code diagnostics. The outdoor unit will provide status indicators and the indoor wall unit and remote control will display error codes. The following is a summary of the codes with explanations...
GREE AC DIAGNOSTIC ERROR CODES
Gree Vireo Mini Split Air Conditioner Error Code F0
Refrigerant Leakage Protection
1) Refrigerant leak(s).
2) Indoor coil temperature sensor not calibrated.
3) Refrigerant flow is restricted (ex. valve, exv, debris)
Outdoor Unit Red Light Indicator - 9 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code E1
System High Pressure
1) Over charged with refrigerant.
2) Blocked or dirty outdoor coil.
3) Extreme outdoor ambient conditions
Gree Vireo Mini Split Air Conditioner Error Code E2
Indoor Anti-Freeze Protection
1) Low return airflow.
2) Indoor fan speed is too low.
3) Indoor coil is blocked or dirty.
Outdoor Unit Yellow Light Indicator - 3 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code E4
Compressor High Discharge Temperature Protection
Please refer to the malfunction analysis (discharge temperature, overload) in service manual.
Outdoor Unit Yellow Light Indicator - 7 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code E5
Overcurrent Protection
1) Supply voltage is unstable.
2) Supply voltage is too low and system load is too high.
Outdoor Unit Yellow Light Indicator - 5 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code E6
Communication Malfunction
1) Communication cable is wired incorrectly between indoor and outdoor units.
2) Indoor or Outdoor control board malfunction.
Outdoor Unit Yellow Light Indicator - Continuous On
Gree Vireo Mini Split Air Conditioner Error Code E8
High Temperature Resistant Protection
1) Incorrect refrigerant charge level.
2) Refrigerant metering device malfunction.
3) Compressor malfunction.
Outdoor Unit Yellow Light Indicator - 6 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code EE
EEPROM Memory Malfunction
Control board malfunction.
Outdoor Unit Yellow Light Indicator - 11 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code C5
System Configuration Malfunction
1) No jumper cap inserted on the control board.
2) Incorrect or damaged jumper cap on control board.
3) Indoor and outdoor units are not compatible.
Gree Vireo Mini Split Air Conditioner Error Code Fo
Pump Down or Gathering Refrigerant Status
Optional Service Mode
Outdoor Unit Yellow Light Indicator - 17 flashes and 1 sec Off
NOTE: All of the Gree Air Conditioner Model Numbers below are applicable for the error codes on this page...
Gree AC Vireo Models: VIR09HP115V1A, VIR12HP115V1A, VIR09HP230V1A, VIR12HP230V1A, VIR18HP230V1A, VIR24HP230V1A, VIR30HP230V1A, and VIR36HP230V1A.
Gree Mini Split Air Conditioner Error Code Charts
Gree Mini Split AC Remote Control Button Names
Gree Mini Split AC Remote Control Icons Display Screen
Gree Mini Split Air Conditioner Air Filter Cleaning Procedure
Need help with error codes on your Gree AC? Please leave a question below and we will be happy to help.
Carrier 42sd7c outdoor kilowatt ?
What are you wanting to know? Kilowatt is a measurement of electrical energy.
WHAT IS FAULT CODE 00 01 Ad on Teco LU160DHRA1 Air Con
Carrier Split Air Conditioner Error Codes - AC Error Code
acerrorcode.com/carrier-split-air-conditioner-error-codes.html
Jan 25, 2015 - REMOTE CONTROLLER FOR AIR CONDITIONER (SPLIT TYPE). Carrier Split Air Conditioner Error Codes. 00-01-02-03. 11-12-04-05.
1helpful
Ac model # 42sd6b er-05 code meaning
Are you trying to run your cooling now? I'm guessing you have a carrier thermostat and that's where this is displaying. It's been awhile since I've came across one but to my vague reculiction that code indicates the outdoor sensor detects low ambient them temperatures which in turn will not allow your air conditioner to run which would make sense this time of year. If you want to run cooling in below 60 degrees temps you must add a "low ambient kit" this shuts the fan down outside to build up higher head pressure without doing this you will just ruin your ac but in your case it won't let you. Google up your Tstats model number and codes if that's not your situation.
1helpful
Er 03 for carrier air conditioner indoor unit 42SD7C Problem
REPLACE INDOOR COIL SENSOR LOCATED AT COOLING COIL "U" BEND.
4helpful
4answers
Top Carrier Heating & Cooling Experts
Ronny Bennett Sr.
Ronny Bennett Sr.
Jay Finke
Jay Finke
Mike Cairns
Mike Cairns
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others