My generac 15kw generator went off on overcrank now the relay just clicks then stops then clicks agin, i have 13 volts at the battery

1 Answer

Anonymous

Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

  • Master 2,006 Answers
  • Posted on Sep 07, 2011
Anonymous
Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Joined: May 17, 2011
Answers
2006
Questions
2
Helped
592735
Points
6261

It could be either your start capacitor or the contactor-relay. Or you could try cleaning the contacts of the relay with an emery board to see if there is a change.

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1helpful
3answers

Generac Guardian Standby Generator 04760 15KW LP won't stay running

Turns out it was the Manual-off-Auto switch that was bad. My DVM showed a voltage drop across the switch. The controller wasn't getting enough power.

One good thing about it was it forced me to really study the schematics to understand how everything worked. I'm now in the process of designing my own esp32 based controller, with wifi connectivity, to replace the stock control board.
1helpful
3answers

My generac generator wont start,making a clicking noise and battery is fully charged

Have somone hold the start button while you measure the voltage across the battery. If it is less than 11 volts, then the battery is bad.
0helpful
1answer

What size wire to hook up a 15kw generator to my house

At 240v, a 15KW generator will produce appx 62A or 31A per 120V leg. Therefore allowing for some overload, a conductor sized for 35A per leg would be adequate, but you should verify local code requirements.
0helpful
3answers

Generac 20,000kW Standby generator doesn't start shows message STOP ALARM OVERCRANKED

Overcrank means that it tried to start and couldn't. It will go through 5 crank cycles and then stop with this alarm. Switch to off, hit enter to clear fault and then try to start in manual. Check to make sure you have fuel and pressure is 11 to 14 in WC.
0helpful
1answer

I have a Generac 15kW air cooled standby generator. I have replaced the battery the spark plug the air filter the oil filter the oil. It is fueled by propane gas. All it will do is crank. Can you please...

You can check for tanks being turned off and of course if there is fuel in the tanks. If further troublshooting is necessary you should likely ask for assistance.
11helpful
8answers

Generac 43903 standby Generator overspeed indicator on starting

I have a generator that did the same thing. It would start and then stop within a few seconds. The more expensive generators have an oil level safety switch to prevent the engine from burning up. There is usually a wire connecting to the switch on the outside of the engine near the oil fill hole. Remove this wire and try to start the generator. If it runs without a problem then it is the switch. You need to remove the switch and take it apart carefully and clean it. There is a small float inside the assembly. When the oil runs low the float allows the switch to short to ground which kills the spark to the spark plug. Hope that helps.

Bob Janelli

I’m happy to help further over the phone at https://www.6ya.com/expert/bob_62dfa2f81bb55288

4helpful
2answers

Overcrank error message

The 'overcrank' error simply means it tried to start but never actually started. It cranked for an extended period. Check the fuel and starting issues you would normally check to start the engine.

If you need further help, I’m available over the phone at https://www.6ya.com/expert/craig_3fa289bf857b1a3c

4helpful
1answer

Start runs shutsdown

Typically caused by the fuel line (LP or Natural Gas) having a lot of air in it. Was your generator just installed, or was there any work done to the gas line of the building / generator? Consult local gas contractor / propane dealer / gas company for assistance in purging the fuel line.

A low battery can also cause this as well as the generator is not able to come up to starting speed quick enough. Try placing a stand alone battery charger on the generator and charge the battery. Also check the air filter as well.

OverCrank condition occurs when generator tries to start itself, or be manually started, and the starter spends too much time turning.

This can also indicate failure of the control board. This will need the expertise of generac technician. Call 1-888-GENERAC (1-888-436-3722)
M-F 7am-6pm Central

Not finding what you are looking for?

978 views

Ask a Question

Usually answered in minutes!

Top Kohler Electrical Supplies Experts

Brad Brown

Level 3 Expert

19187 Answers

john h

Level 3 Expert

29494 Answers

ADMIN Andrew
ADMIN Andrew

Level 3 Expert

66820 Answers

Are you a Kohler Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...