LG LP126HD3A Air Conditioner Logo
Posted on Sep 06, 2011
Answered by a Fixya Expert
Trustworthy Expert Solutions
View Our Top Experts
LP126HD3A rated for 265 volts AC single phase I have 240V ac single phase, how can I use this unit on 240V ac
Steve
Level 3:
  • LG Master 3,290 Answers
  • Posted on Sep 06, 2011
Steve
LG Master
Level 3:
Answers
3290
Questions
Helped
1128227
Points
12184
You'd need to supply a "Buck-Boost" transformer to do this properly. Technically, the 265 VAC is one hot leg and neutral of a 480 VAC 3 Phase Y system that measures 277 VAC. The 265 number comes from this:
265 is the standard nameplate voltage for a 277 volt motor or AC unit.
230 is standard name plate for 240.
200 is standard name plate for 208
460 is standard name plate for 480.
110 is standard name plate for 120.
Most electricians call the hot leg / neutral circuit "277V AC".
Some popular "Buck-Boost" transformers will convert 208 to 240 and 240 to 208 volt systems, and 240 to 277 and 277 to 240 volt systems - among many other variations. These are auto-transformers as the primary secondary windings share a connection. KVA ratings differ significantly from name plate because of this fact. You should contact a qualified electrician to not only size, but wire the transformer for you. Failure to install a Buck-Boost transformer - and running this unit on 240V AC mains will cause premature failure of motors - fans and compressor due to overheating. This can also result in a fire hazard.
I hope this helps and good luck!
I got a Generac GP8000E generator from the US. The Manual says the generator supplies electrical power of 120 and/or 240 volts AC, 30amp, single phase, 60Hz. I need an output of 240V 50Hz. Help Please
You need a frequency converter - however, these are not cheap since they are intended for industrial applications - usually rated to drive motors. Depending on the device that you are driving, you might be able to adapt it for a DC input and convert the generator output to DC, or modify it to accept a 60 Hz input.
Frequency Converters
AC Power Supplies Frequency Converters
Digital inverter generator has no 240 volt output
Most power inverters are strictly single-phase. Meaning true 120V or 240V, and no splitting or duplication. It sounds as if your inverter is a single phase 120V, and likely is not stackable on the AC side.
I recommend looking for a Low Frequency Split Phase power Inverter if you want both 240 and 110 volts.
Aug 09, 2013 • Vacuums
2helpful
Where can i find ac motor connection diagrams, specifically, single phase forward and reverse, and 415v motor to 240v power diagrams? thanks andy
there is no motor that is single phase with 415 volts only 240 volt or 120volt and you cannot use a 3 phase motor on single phase it will just fail to start buzz and burn it up .single phase motors have capacitors 3 phase motors do not
I am working with a Dayton 2YU39. The name plates states that it has to be powered by 208 volt system. There's a 3-phase panel and a single-phase panel. The 3-pahse panel L1 to ground is 118 volts. L2 is a...
Here's what I think but you will have to check it out...
The fan motor in the 39 heater is a 120V fan there fore it cannot be hooked to the 240 which potentially could have the high (wild) leg as one of the fan legs...
The 240V 36 unit probably has a 240v fan motor....
Now if you were to make sure that the leg that fed the motor was a 120V to ground leg then you will be okay...
Hope you understand where I was going with this...
heatman101
I have a miller cp 300. It is wired for 3 phase power. I need to hook it up to 230 volt power. How do I do this correctly.
You cannot do this... 3 phase and single phase cannot be inter used... see 3 phase is 440 V AC, single phase is 230 Vots AC. This is unless the unit has Dual capability, in this case the wiring could only be wired to a Single Phase. of the unit. You will need a slow blow breaker of the correct rating and also the cable must be similarly CURRENT rated. If it IS only 3 phase, you can purchase after market single phase to 3 phase converters, that will allow you to plug the 3 phase into a single phase circuit and work, they quite costly though.
Is posible run a single phase electric motor from a source three phase 120/208 wye connection the motor is rated 230 volts AC
It is indeed possible to use ONE Phase to run a motor, You simply use One Phase and Neutral. BUT ONLY if the 3 phase is Double, more or less, the required usage Voltage, EG: 440 3 phase, will be OK, for 220 single phase, . But 220 3 Phase,will not run a 240. single Phase. So in your case is suspect not, it really will do no harm to try though. it just wouldn't work, if not enough "juice", be careful.
http://en.wikipedia.org/wiki/Three-phase_electric_power
We have a Carrier mini split AC that we are wiring on a portable office that will be going to a foreign country, the Carrier #38QG24-H. This unit's voltage specifications is 200-240volts, single phase, 50...
please 200- 240 volts is a standard for all and for the breaker is depending of the country if 120 v single phase you will install as usa if 220 v single also you can connect you breaker but the problem is some countries are not 50 hz comfirm the unit is 50/60 hz.
1helpful
AC Breaker trips and AC Fan turns slow.
Sounds like you have a bad capacitor for your squirrel cage fan , now as for the a/c unit sounds like you have a direct short in compressor to ground or leg to leg , check all wiring to make sure that it is not grounding out or melted together.
10helpful
Heat load calculation
Here are a few ways to calculate your BTU's.
Get ready to use that algebra you thought you'd never use.
1 Ton = 12000 BTU's
400cubic feet per minute (CFM) = 1 Ton on standard ac units (300 is an absolute minnimum)
BTU's air heat = difference in temp. ( ∆T ) x 1.08 x CFM
∆T = BTU's / (1.08 x CFM)
i.e. 65F entering your unit and 93F air leaving on a 12000BTU unit.
∆T = 28
CFM = 400
28 x 1.08 x 400 = 12096BTU's
Another way...
Electric heat calculations.
BTU's = KW (killowatts) x 3413
Watts = Volts x Amps (single Phase) Most Homes))
Watts = Volts x Amps x Phase (this is for three phase units.)three wires and a ground))
120 volts 30 amps single phase (common)
120 x 30.0 x 1 = 3600 or 3.6KW 3.6 x 3413 = 12286BTU's
1helpful
4answers
What amp is the plug?
This is a 220 unit and it must be plugged into a proper 220 volt plugin.
Top LG Heating & Cooling Experts
Mike Cairns
Mike Cairns
MattS1978
Level 1 Expert
Jay Finke
Jay Finke
Are you a LG Heating and Cooling Expert? Answer questions, earn points and help others