I have Kohler 12Res generator,sometimes it runs fine and sometime it runs for 5 min and then shut down with error code UU (under voltage).I cant find authorized service center in Pakistan.Please help me to solve this problem. Thanks

1 Answer

Anonymous

Level 1:

An expert who has achieved level 1.

MVP:

An expert that got 5 achievements.

New Friend:

An expert that has 1 follower.

Hot-Shot:

An expert who has answered 20 questions.

  • Contributor 41 Answers
  • Posted on Sep 06, 2011
Anonymous
Contributor
Level 1:

An expert who has achieved level 1.

MVP:

An expert that got 5 achievements.

New Friend:

An expert that has 1 follower.

Hot-Shot:

An expert who has answered 20 questions.

Joined: Jul 04, 2011
Answers
41
Questions
0
Helped
26570
Points
53

If it has a couple hundred hours or more, try cleaning the slips rings on the back of the rotor shaft. They should be very shiny and not black or polished looking.

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

Kholer power systems generators 18RESL auto shut down code UU

UU is generator under voltage. Check to see if it does it without laod also. if it does you will need a pro to check and ohm the rotor and stator for shorts
1helpful
2answers

My 3.5 kw kohler marine gen starts and shuts right off throwing code uu (under voltage) last season it did this and sometimes showed loc (loss of coolant) but never appeared low or showed sign of coolant...

Check that when you run it, it is not in fact making correct voltage (within about 10% is good), also make sure the engine is coming up to full speed, 3600 or 1800. You could check this with a multimeter that measure hertz. On the main output leads when the genset is running make sure it is getting close to 60 hz. or if you are in an area that uses 50 hz. check for that respectively. There are a couple things that would affect this, one would be your SCR module. There is a test procedure for this which you could find here. http://www.scribd.com/doc/50171916/tp6196-1 . I don't work on marine units, mostly standby so these manuals are for residential. Check your fuses, could even go as far as checking the wiring in the back and wiring and condition of the brushes and sliprings. These actually build field voltage to make 240 or 120 volts whatever your unit is configured to make. The brushes need to sit flat on the slip rings and on a unit with 10 hrs. the sliprings I can't imagine would be very dirty but check that as well. If you have an ADC2100 controller use this manual to go into the controller to verify that it is set for the correct voltage that the machine is built to make. The only other fairly simple thing to check that I've had issues with is if Kohler mounted a fuse block on the side of the cabinet mounted to the genset with no vibration isolation. Check these fuses while attempting to run the unit and make sure you getting steady voltage out of them as sometimes they will vibrate causing pulsed voltage to come out of them and can give you an intermittent UU, UF, or OC fault (undervoltage, underfrequency, overcrank).
0helpful
1answer

My gen starts and runs for 1 min or so then dies restarts then dies again and again. if i start it under load ( turn on air con) it will run for 10 min then die allen

Is there a fault?? All UL listed generators including Kohler are required to lockout on a fault on shut down. This really sounds like a problem with your 2-wire auto start connection between your automatic transfer switch and genset. RDT model automatic transfer switch it is the 2 middle wires on the green connector and terminals 3&4 in the generator. close to run and open to shut down. Any open at any time will cause the unit to shut down. The 12 will shut down instantly upon an open because your 5 minute cool down is built into the transfer switch.
2helpful
1answer

The monitoring system of our Kohler propane generator has sent a "UU" message. What does this mean as it causes the generator to shut down 10 seconds after starting? Also how can this be...

The monitoring system of our Kohler propane generator has sent a "UU" message. What does this mean as it causes the generator to shut down 10 seconds after starting? Also how can this be corrected?
2helpful
1answer

Code UU

Here is the code explained direct from Kohler's manual. I'd disconnect the generator load first.
UU Undervoltage Shutdown occurs if the voltage falls below 80% of the nominal system voltage for more than seconds. Check wiring and connections.
Reduce the load and restart the generator set. —
Check wiring and Check controller configuration, system voltage
and frequency (parameter UU).

Check AC voltage and adjust, if necessary. 5.7
Replace the SCR module and test voltage again. 4.9
Separately excite unit. 5.2
Check stator continuity

See web site for manual :http://www.kohlerpower.com/onlinecatalog/pdf/tp6196.pdf
1helpful
3answers

I have a Kohler 12RESM1 propane generator with oc/uu code

U need to make sure that the relay driving ur auto start stay closed all thru the crank cycle.
0helpful
2answers

I have a Kohler 12RES, 12.5kw genset. Less than a

check connections on speedsensor or take down rpms must be a screw or bolt on de fuelpump
1helpful
1answer

UU undervoltage kohler 20kva

call koler but ui think is meant high heat as in the thermal circut is shuting you down or low oil
could be a couple of things best bet call kohler
0helpful
1answer

UU lowvoltage error code residential generator

Could be the battery voltage. If your battery is not charging properly, the controller on the unit can do some funky things! Exactly how long does it run for? Is this in auto or manual mode?
Not finding what you are looking for?

1,560 views

Ask a Question

Usually answered in minutes!

Top Kohler Electrical Supplies Experts

Brad Brown

Level 3 Expert

19187 Answers

john h

Level 3 Expert

29494 Answers

ADMIN Andrew
ADMIN Andrew

Level 3 Expert

66915 Answers

Are you a Kohler Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...