20 Most Recent
Honeywell Programmable Thermostat Heater - Page 8 Questions & Answers
Trouble shoot rth2308
on pages 26 and 27 of the manual it clearly states that the unit has a safety device installed in at the doesn't allow the heat and the air to be turned on one right behind the otherif you are testing out both air and heat expect about a 15 minute delay between both of them that is to protect your system just leave the unit alone you don't update by itself and it'll start working correctly in about an hour
2/23/2015 9:21:14 PM •
Honeywell...
•
Answered
on Feb 23, 2015
AC wont kick on....
The first thing to check is your breaker box. There should be one double breaker for the air handler unit, that's the inside unit, and one double breaker for the compressor, that's the outside unit. Check both breakers. If you're not sure if they've be thrown, click them toward the outside of the breaker box (off position) and then click them toward the inside of the breaker box (on position). If the breakers are on and you still are not getting any A/C take a look at your compressor, (outside unit). If the fan is running at least you're getting power. However, your compressor down inside the unit may not be getting power or it may need to be replaced. The compressor has a start-up cap. If this cap goes bad or the wires from this cap fry or corrode away, this will also keep the compressor from starting but the fan will still run. If the fan is not running it could be caused by a faulty relay inside the compressor cabinet. This relay is supposed to open and close based on a low voltage signal from the thermostat. I believe it's roughly 24 volts. This relay switches on and off the 240 volts for the compressor and the compressor fan. Often this relay goes bad or the wires leading up to it fry. If you?re going to work on the unit yourself make sure all power is shut off. There should be a shutoff switch on the outside wall near the compressor. I?d also shut the breakers off.
2/21/2015 5:55:58 AM •
Honeywell...
•
Answered
on Feb 21, 2015
Honeywell - cm61ng- Keeps going on and off all night
Instructions on how to turn off your optimum start:-
Turn off ‘Optimum Start’
Step 1 Put the thermostat in the OFF position.
Step 2 Press 3 buttons together (at the same time) which are the INFORMATION BUTTON (i) and PROGRAM BUTTONS 3 & 4.
This will show a code of ICL 1 – now let go of the buttons.
Step 3 Press PROGRAM BUTTON 2.
This will now show a code of 30t 1
Step 4 Press the + BUTTON (on the left of the display), tap through until you reach 15 OP 1
Step 5 With the TEMPERATURE DOWN BUTTON; change the 01 to a FLASHING 0. Confirm the FLASHING 0 with the INFORMATION BUTTON ( i ). The 0 will now be static.
Step 6 Put the Thermostat back in the ‘AUTO’ position.
‘OPTIMUM START’ is now switched off.
2/13/2015 6:40:53 PM •
Honeywell...
•
Answered
on Feb 13, 2015
Furnace reads system on but furnace will not run
It is definitely a furnace problem. Once you turn the thermostat up above room temp, it closes a switch and sends power to your burner, (gas or oil). It would seem more like a problem at the burner that is causing you problems. If you do not have experience with heating equipment I suggest you call a local repair man. Hope this helps a little
10/30/2014 2:30:15 AM •
Honeywell...
•
Answered
on Oct 30, 2014
Dip switch settings rthl2310
Check for cold air inside the wall behind the thermostat, a cold wall, and area that is getting hot or cold air blowing on the thermostat. Last, the heater may not be compatible with some digital thermostats.
Honeywell Customer Care toll-free at 1-800-468-1502.
8/31/2014 3:21:19 PM •
Honeywell...
•
Answered
on Aug 31, 2014
Not finding what you are looking for?