Ruud UBHC Air Conditioner - Answered Questions & Fixed issues

0helpful
3answers

Ruud Electric Furnace Cannot Reach Setpoint - "Watt Restrictor"?

unfamiliar with watt restrictors.
heat strips have 2 safety devices, a thermal overload, they get to hot they shut off, cause not enough air flow increase fan speed this device is auto reset. a fusible link a fail safe to thermal over load, no reset and sometimes replaceable. if this does not help would like to ask you a few questions. one of the buildings i take care of has 200 + reem/ ruuds all electric heat. if a part is defective replace, please do not by pass. safety frist.
2/5/2020 6:13:08 PM • Ruud UBHC Air... • Answered on Feb 05, 2020 • 1,824 views
0helpful
2answers

Heating unit blows warm air then turns to cold air

it sounds like unit could be kicking out the low pressure switch or if it is a electric furnace it could be the sequincers
3/13/2019 2:57:31 AM • Ruud UBHC Air... • Answered on Mar 13, 2019 • 504 views
0helpful
1answer

Is this air condition unit energy effeciant

If sold in the USA in the last five years the answer is yes.
6/8/2018 7:43:49 PM • Ruud UBHC Air... • Answered on Jun 08, 2018 • 92 views
0helpful
1answer

RUUD UBHC-17J14SFA HEATING PROBLEM. Is there a way

The blower speed can be changed somewhat the same way , but it will have to be rewired using one of the extra capped wires for a lower speed. That is if the other wires were not clipped and just capped
1/8/2018 4:14:42 AM • Ruud UBHC Air... • Answered on Jan 08, 2018 • 685 views
0helpful
1answer

Is a RUUD UBHC-14J11NFH a heat pump?

Ruud UBHC-SERIES is a HEAT PUMP AIR HANDLERAND FAN COIL UNIT Compressor and condenser not includedSpec sheet go herehttp://yaunco.com/pdfs/rheem/ubhc_specs.pdf
1/6/2018 10:32:27 PM • Ruud UBHC Air... • Answered on Jan 06, 2018 • 413 views
0helpful
3answers

Uotside unit blowing cool air but hot on the inside

It sounds like you have a unit called a heat pump. When a heat pump unit is in cooling mode the outside unit blows hot air and the inside unit blows cold air. If the outside unit is blowing cold then the indoor unit is most likely blowing room temperature or warm air. It sounds like the thermostat could be controlling incorrectly or you could have a failed reversing valve which is the device that switches the unit from heating to cooling mode.
10/11/2017 10:05:55 PM • Ruud UBHC Air... • Answered on Oct 11, 2017 • 1,077 views
0helpful
1answer

I have a Ruud Model UAFD-036JAS Air Achiever 9 split system, when i try to turn on the a/c, nothing happens. I've replaced the contactor, run cap., put in a starter cap for the compressor, replac

If you push the contactor and it runs why replace all that stuff??? You have to figure out where your 24 volts stops on its way to the condenser contactor. wire red green and yellow together at tstat, this should bring on indoor fan and condenser. if idf runs but cu does not you have an issue either going outside or a pressure switch is tripped. if nothing runs you have no 24, either a blown fuse, tripped float or bad transformer. If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
10/3/2017 11:49:18 AM • Ruud UBHC Air... • Answered on Oct 03, 2017 • 525 views
0helpful
2answers

Rudd silhouette ii blower

Send direct power to the blower by bypassing relay . See if motor runs If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
7/19/2017 7:17:20 PM • Ruud UBHC Air... • Answered on Jul 19, 2017 • 347 views
0helpful
1answer

Ruud gas Furnace UGPH 07EAUER cycles properly

Whew... Most likely... Your part number (look it up) RUUD 47-25349-?? (LIKE: 02, 03, 07... etc). (typically: $10 -$20 range... easy job) On eBay: A bit slow getting this answer out on the table... Sorry anonymous. BUT for the "over-temp" condition... Forget the wall THERMOSTAT. There's usually a switch to option the "DEPTH" of your heating cycle (Look up Owners GUIDE for your SPECIFIC MODEL). The "cool down"... (if there is one) would more likely be you heaters OWN (fan) THERMOSTAT... It SHOULD not be getting that much RESIDUAL heat (possible plenum failure... but hopefully just the switch). Here you have to ask yourself... Is IT TIME to get your heater PROFESSIONALLY inspected... Pacific Gas & Electric used to do that for FREE... (but in this new, improved UTILITY climate we enjoy today... I doubt they''ll do more than TAKE OUT a few blocks in SAN BRUNO for FREE anymore... (you might want to check... (Same DEDIATED workers w/ really poor Management)). (My opinion: FAT CAT, CRONY, bought & well-paid EVIL/corrupt Government "oversight" (CPUC)). There SHOULD also be a HIGH TEMP fuel shut off "SAFETY" thermostats.. All these should only be handled with skill & knowledge... as GAS APPLIANCES can be quite dangerous in the WRONG HANDS...!! I am just saying...!! I'm here daily... Comment me back if unclear. Happy hunting. Carnac the Magnificent Y
5/10/2017 11:51:29 PM • Ruud UBHC Air... • Answered on May 10, 2017 • 588 views
0helpful
1answer

"RUUD Achiever 90 Plus" Propane

Hello bikejocky, MOST LIKELY you have a "hot surface" element with a tiny crack in it... About 25 years ago... I put one of my poor abused fingers on the element to see if it was at all warm... In so doing I touched the spot where the crack was... and it did INDEED have a full 120 volt, 60 cycle AC current waiting for my FINGER to complete the circuit... (not a recommended procedure) My 25 year old RHEEM... finally kicked it. I keep spares... and bought 2 more when I used the last Since these parts are pretty cheap... I get spares 62 22868 93 Rheem 62 22868 93 Hot Surface Ignitor Take a look... There are two basic configurations The WISEST APPROACH is to use a "meter" to verify the "line current" is present (not finger) and check the "SURFACE" for continuity. Once you copy the number DIRECTLY from YOUR OWN part... look it up... internet... eBay and AMAZON (like Robert Shaw #41-408). http://www.ebay.com/itm/ROBERTSHAW-41-408-Hot-surface-ignitor-NORTON-271N-/121727955205?hash=item1c578d3105:m:mJR3I8e9mTI60A-dtmvdVrw >> It is the plug & mount that is important...!! (consider that spare you always wanted (If you get it... you will probably never need it)). ~~ The cycling limit & fan (never touched a RUUD... (so... I presume)) is to clear accumulated GAS FUMES to avoid any explosive situations. I do know RHEEM... (ERGO... I have every confidence) ((RHEEM & RUUD, in my opinion, are design twins)). Carnac the Magnificent
5/10/2017 2:05:19 PM • Ruud UBHC Air... • Answered on May 10, 2017 • 238 views
0helpful
1answer

Outside fan not turning inside fan running

Very impressive!! This button you are referring to is a contactor. When your tstat calls for cooling it sends 24 volts out to the contactor therefore pulling the contactor in completing the circuit for the fan and compressor. Usually this doesn't work when a safety switch is preventing the 24 from getting to the contactor. Either it's not getting a signal from the tstat or one of your safeties are tripping (high or low pressure) or the float switch on your drain line at the air handler is wired in to only stop the condenser from working rather than the tstat. A multimeter would be extremely helpful for you to determine where the voltage is stopping. Check your drain first, I don't suggest your patented rock idea, it's not running because of a safety. Good Luck , let me know!! If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
4/30/2017 2:26:43 PM • Ruud UBHC Air... • Answered on Apr 30, 2017 • 106 views
0helpful
1answer

Model #uobc-084qbea. It's summer time and the AC

The evaporation cooler tray can get build up of dust and debris and plug the drain..
4/27/2017 12:16:48 AM • Ruud UBHC Air... • Answered on Apr 27, 2017 • 175 views
0helpful
2answers

Ruud achiever 90 condensation overflow

Not a furnace guy but I do know that your drain should be insulated. Gotta figure out if it's water from the drain leaking or actual condensation dripping from the outside. If sweat, it needs insulated. Good Luck. If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
3/11/2017 12:50:00 PM • Ruud UBHC Air... • Answered on Mar 11, 2017 • 2,098 views
0helpful
2answers

Bryant air condition fan outside not coming on

Check breaker for outside unit Also check to see if you ahve afloat switch on the inside air handler. Located under or in front of unit. It may be full of water and tripped. Blow out drain if tripped.
3/7/2016 9:42:12 PM • Ruud UBHC Air... • Answered on Mar 07, 2016 • 1,110 views
0helpful
2answers

Scroll compressor has a clunking

2/16/2016 6:14:22 AM • Ruud UBHC Air... • Answered on Feb 16, 2016 • 402 views
0helpful
1answer

Thermopompe stop end start constanly

going off on safety. could be drawing to many amps or compressor overheating
8/26/2015 11:29:43 AM • Ruud UBHC Air... • Answered on Aug 26, 2015 • 140 views
0helpful
1answer

Emergency Heat won't turn on

thermostat, relay or heating element issue
8/17/2015 9:37:31 PM • Ruud UBHC Air... • Answered on Aug 17, 2015 • 113 views
0helpful
1answer

Payne py1pnb036090abaa

change motor.
8/17/2015 9:35:22 PM • Ruud UBHC Air... • Answered on Aug 17, 2015 • 109 views
0helpful
1answer
0helpful
1answer

I have a RUUD A/C model UBHC-17J11SFF. The consensation pan has a crack. Can the pan be repair/removed without cutting the copper tubing?

not really you have to remove coil to replace pan. if there is room you can abandon that pan and put another under it.
8/17/2015 4:48:54 PM • Ruud UBHC Air... • Answered on Aug 17, 2015 • 402 views
Not finding what you are looking for?
Ruud UBHC Air Conditioner Logo

779 questions posted

Ask a Question

Usually answered in minutes!

Top Ruud Heating & Cooling Experts

Brad Brown

Level 3 Expert

19187 Answers

Ronny Bennett Sr.
Ronny Bennett Sr.

Level 3 Expert

6988 Answers

john h

Level 3 Expert

29494 Answers

Are you a Ruud Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...