20 Most Recent Honeywell Biasi B10-3 Boiler ,riello Burner Questions & Answers

0helpful
2answers

I have a riello 40 burner it fires for 2 seconds then cuts out what could be the problem

If it actually fires up and you have a flame for 2 seconds and then it shuts off, I'd bet that the photo cell is either dirty or has failed. If it is dirty, it suggests that the burner has been neglected for some time and probably is in desperate need of a tune up. The photo cell is located under the ignition transformer and is aimed into the combustion chamber to see the light created by the flame from the burning oil.If it is clean, the photocell has likely failed and will need to be replaced. If it still runs the same way after photocell replacement, it is probably related to the primary controller or one of the other safety devices. Is this a forced hot air or hot water system?
12/28/2021 10:31:33 PM • Honeywell Biasi... • Answered on Dec 28, 2021
0helpful
2answers

Biasi boiler not heating house thermostat can be set on 80 house will not get warmer than 55

Check thermostat since unit is working but is shutting off prematurely.
2/15/2016 5:23:12 PM • Honeywell Biasi... • Answered on Feb 15, 2016
0helpful
1answer

I have a riello burner 40 it will fire and come to temp but wont refire, goes into lockout

My first guess would be that it sounds like a clogged oil filter, air in your fuel line, is piping overhead, or leak in a fitting or connection causing it to loose it's prime when running. I have also seen primary controls that are faulty do this, watching the complete cycle of the run time will give you more clues as to when the control actually locks out. Does it lock out during the run cycle as the boiler reaches temp.? If so,check for oil line and suction issues as stated above. If it locks out on start up after reaching boiler set temperature, if hitting reset right away burner doesn't start and lock out occurs with no motor engaging, check motor (Note: Some motors when HOT will not kick in when powered, but after they cool down naturally they start, motor shaft may also be bound up tight, replacement is necessary) if burner motor spins but does not fire, check for fuel flow to the nozzle, be sure oil is pumping to the nozzle, if it is, clean cad cell eye, and check transformer for spark, if all is good.. replace primary control. Disclaimer: Of course all this information is technical troubleshooting information and should be performed by a Licensed Technician, not knowing how to properly test for flame failure can cause injury, fire or worse! Consult a technician in your area if you are not proficient at oil burner repair!
12/13/2014 1:25:32 PM • Honeywell Biasi... • Answered on Dec 13, 2014
0answers
0helpful
1answer

Riello burner

You need to measure the manifold pressures before and after the gas valve and adjust accordingly to fuel used, 3.5" NG or 11" Propane.
11/7/2013 2:42:06 AM • Honeywell Biasi... • Answered on Nov 07, 2013
0helpful
1answer

I have riello oil burner put oil into a empty tank

is the filter clean u might of picked up sludge in bottom tank also blow out the supply lines and re fitt try again
10/12/2013 9:18:39 PM • Honeywell Biasi... • Answered on Oct 12, 2013
0helpful
1answer

How do I turn the timer off on my Honeywell st1501

Timer setting is given of page 11 of user manual User manual Honeywell CT1501 (English - 28 pages)
10/24/2023 1:21:50 PM • Honeywell Water... • Answered on Oct 24, 2023
0helpful
2answers

Loud buzzing sound from qas valve

replace it
10/14/2023 5:19:06 AM • Honeywell Water... • Answered on Oct 14, 2023
0helpful
1answer

On my Honeywell thermostat control for water heater the red light is not working at all so pilot won't stay lit. No status light on at all.

Some time ago I had that happen and because of the age my repair man said it would cost too much to repair it. The problem was a worn out thermostat.
9/10/2023 8:35:18 PM • Honeywell Water... • Answered on Sep 10, 2023
0helpful
1answer
0helpful
1answer

I have a Whirlpool model N50T61-403 water heater. I have no status light on the Honeywell controller, & no pilot

Gas valve might be bad... The honeywell gas valve for atmospheric models is generic and can be replace without removing from heater. Following links have resources: http://waterheatertimer.org/How-to-replace-Honeywell-gas-control-valve.html http://waterheatertimer.org/How-to-troubleshoot-gas-water-heater.html#honeywell
10/28/2019 5:33:21 AM • Honeywell Water... • Answered on Oct 28, 2019
0helpful
1answer

Go to Johnston and starley Honeywell warm air system . Water heater pilot light on but heater got no flame

This is likely a gas valve issue. Call a repair person, it is not recommend you repair it as there is a danger of explosion.
6/7/2018 3:05:20 AM • Honeywell Water... • Answered on Jun 07, 2018
Not finding what you are looking for?
Honeywell Biasi B10-3 Boiler ,riello Burner Logo

12 questions posted

Ask a Question

Usually answered in minutes!

Top Honeywell Water Heaters Experts

Paul Carew

Level 3 Expert

3808 Answers

SmartAviator
SmartAviator

Level 3 Expert

1124 Answers

Bonded Repair

Level 3 Expert

407 Answers

Are you a Honeywell Water Heater Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

View Most Popular

Honeywell Water Heaters

  • Honeywell Water Heaters

Most Popular Question

riello oil burner put oil into empty

  • Water Heaters
Loading...