20 Most Recent
Liebert (GXT2-10000T230) (GXT2-10000T230) UPS System Questions & Answers
Gxt2-10000t230 no charge
1.check the battery voltage if it rise up,if risen its shows the batteries are charging.2.after powering mains,wait for the ups to transfer to ups on mode,then disengage the batterry breaker,ups should still continue to powerup if charger is ok but if ups shutdown during the transition,then the charger is not on.or call me 08082245266.
11/5/2015 11:32:25 AM •
Liebert...
Answered
on Nov 05, 2015
Liebert gxt2-10000t230 low batt,bypass light flashing,no output,shutdown after a minute
Test outlet power by switching the unit to manual bypass and breakers off.
If power is supplied OK and the filter board repaired OK then restart the unit starting with the breakers supply to unit,battery confirm the display is on and static bypass led also on then switch back the bypass knob to normal and press the on button to switch the unit to normal.
Give the batteries time to charge 12hours then you can test the unit on backup mode.
12/8/2014 8:23:00 AM •
Liebert...
Answered
on Dec 08, 2014
The UPS only flashing the
You have a major fault. Try to reset the logic. UPS has to be off including the batteries. Call me at Gruber Power Services for free tech support. 800-658-5883 x256 ask for Eric
8/24/2011 6:23:47 PM •
Liebert...
Answered
on Aug 24, 2011
Need to monitor status of Liebert 150 KVA UPS
Try to find your manual here in this site. Choose your Product Category, Product Application, Application Type and Specific Product. After that you can download the manual. Hope this helps. "http://www.liebert.com/servicesupport_pages/ProductDocumentSelector.asp"
3/9/2022 9:09:22 PM •
Liebert...
Answered
on Mar 09, 2022
Liebert gxt3 1500
staticbypass is actvated by the main control card via the press button swith,to transfter back to online mode its still the control card that do the timing for the transition to take place so i would suggest you test with another control card or try and be patient and see if it takes longer time to transfer back to online mode.
11/5/2015 12:15:13 PM •
Liebert...
Answered
on Nov 05, 2015
Battery over voltage
did you replace battery recently if yes,what is the ah of the new one you moved in,hope its the same ah with the one you moved out,if all batteries are new try to self drain batteries with battery tester and retest again with ups.
11/5/2015 11:45:53 AM •
Liebert...
Answered
on Nov 05, 2015