Coleman Propane Forced Air Heater w/Electronic Ignition (50,000-80,000 BTU) - Page 4 Questions & Answers
I'm getting the 2 flashing light indicator, says
first thing i would do is follow the short rubber tub from the draft switch to the furnace. pull the hose off the furnace body and run a paper clip, or such, into the hole. replace the hose and see if that helps. check the vent ing for blockage and then replace the switch
Turning heater on : combustion air switch failed to close?
This air switch proves that the inducer motor is running and moving air. If not, check to make sure that the inducer motor starts and that the flue is free of restrictions.....eg. bird nest, ice/snow, or some other critter that found a new home.
Furnace shuts off
Defective combustion air switch. The 3 blinks are an error code. You didn't say, but I'm guessing you have a Coleman Evcon. They had alot of defective Combustion air switches. Your specialists were not that.
Can a wrong gas valve cause a heat exchanger to become deformed?
Hello, I would get another company to come out and check the Furnace. The gas valve starts and stops the flow of gas to the burners and if the gas pressure is not correct, it could be overfiring the burners. So yes they are related. but this is the fault of the service company and if they make mistakes by installing the wrong gas valve then I would look for a differant company.
Blower motor not coming on for electric heater
Talk about a misnomer? Electric heat works way diff than gas heating. On electric heat multiple strips and a fan of course. But if they all come on at the same time then the breaker would trip so they use a sequencer for that job. Gas heat uses a bi-metal probe which twists around and turns the fan on when the temp reaches 110 in the plenum. Yall either have a bad fan or capacitor OR the thang that turns the fan on ain't doin it. If you need further help, reach me via phone at
https://www.6ya.com/expert/dan_73bbd84fe1d95b61
Blower motor not coming on for heater
Hello, the blower motor typically will not turn on if the capacitor is bad, control board is bad, or motor is shot. If there is voltage coming from the board to motor than that eliminates the board. If you can spin the blower wheel by hand and it starts up then the capacitor is bad and must be replaced. If you have power to motor and capcitor is good that only will leave the motor as being shot.
Coleman evon BGU10016A put in new ignition light and still wont heat up, what next
Check to see if you are getting power to the ignitor... if not then the ignition control module is bad or there is another control that is keeping the control module from trying to light the furnace...Check for 24v power going to the control module and also check that all of the saftey controls are closed and completing the safety circuit...are you getting any flashing LED'S on the control module?
Need yo connect thermistat to coleman model
Hi,Here is a list of each common terminal and what their commonly used for. Alsolisted is what colors are commonly used. NEVER ASSUME these are what
youhave. Verify all your wires by following each to each piece of equipment. Thiswill help you to be able to match your equipment with the terminal.Here is the rest of the tip that I wrote...
Thermostat Wiring and Terminal Designationsheatman101If you have further questions, then comment back to me...