In heat mode but heat strips don't come on and the air handler fan dose not turn off

Maybe a bad sequencer.unplugged wire from sequencer and see it unit shut off .Sequencer is typically a relay
2/23/2018 11:06:02 AM • Goodman... • 991 views • 0 helpful votes
0helpful
1answer

Goodman GS9 blowing air but not getting hot

Does furnace fire up ,if not you have a issue with your furnace and not thermostat
2/12/2018 1:54:02 PM • Goodman... • 200 views • 0 helpful votes
0helpful
1answer

Heater fuse blows when ac is turned on

poor Wire connection on the breaker? Is the wire screwed down tight? SHUT THE MAIN OFF FOR SAFETY, then pull the breaker off the buss bar and inspect the bussbar and bottom of breaker for any burn.

It’s helpful to also use and ampmeter to check equipment amp draw vs. the amp rating on the equipment tag.
1/27/2018 3:18:02 PM • Goodman... • 132 views • 0 helpful votes
0helpful
2answers

The thermostat is set to heat at a temp of 68

The burners are not igniting and the timer turned on the blower thinking the burners were already lit by then. You have a burner/ignition problem. Either the ignighter or themocouple is bad
12/31/2017 3:30:04 PM • Goodman... • 238 views • 0 helpful votes
0helpful
2answers

Problem: Pressure Switch Failure to close

Hello, The t-state set to fan "ON" will only cycle the fan to turn on only nothing else. "Auto" is where you always want the t-state on when you want to have heat and have the fan cycle off automatically after the t-stat has reached set point. As for the press switch, there can be two things that will cause the pressure switch not to close. 1: obviously the switch itself and 2: the inducer fan, this has the rubber tubing that connects to the pressure switch. When you call for heat, the inducer fan ( small fan with black plastic piece that spins ) is the first to turn on, this fan makes sure any left over exhaust air/gases are vented out before the burners turn on, it also stays on the entire heat cycle to exhaust the gases. The pressure switch needs proof of air so the pressure switch closes with the vacuum that is being created by the inducer fan in that rubber hose that is connected to the pressure switch. This allows the furnace to know " my induce fan is working, lets proceed". So, I would make sure your inducer fan is working. if you don't see it working then I recommend using a multi-meter ( VAC setting) and checking that you have 120volts supplied to the inducer fan. if you don't, then you need to work backward from there and see why you don't. If you do verify 120volts at your inducer motor, then more than likely it failed and will need a new one. Witch out this, your pressure switch wont close. If your inducer fan is working fine then make sure you have 24vdc across you pressure switch (again with a multi meter but with VDC setting not VAC). 24vdc in and 24vdc out. If you only have 24VDC in but not out, then you pressure switch may be stuck open. ( This is if your inducer fan is working properly). I hope this helps. Sorry for the long response. I just don't like people changing parts and wasting money.
9/28/2017 3:30:03 AM • Goodman... • 437 views • 0 helpful votes
0helpful
1answer

Goodman furnace GMT115-5B Turn fan to on on

Bypass the tstat first but that's where I'd be leaning. If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
8/14/2017 3:51:03 PM • Goodman... • 311 views • 0 helpful votes
0helpful
1answer

Where can I find the specs for an earlier Goodman heat pump?

You say 2 to 3 years... I'm assuming the unit is older than that. Especially being r22. What about the first 10 years??? Normally you will get 400 to 500 sqft per ton of cooling, but, that depends on heat load calculations. If the unit wasn't big enough you would have had this issue 10 years ago, not when the system kept running low on refrigerant. At first guess I would say a 2 ton unit is not big enough but if it worked fine for 10 years...wuth all that in mind, if it were me, (a seasoned professional) I would spend 1800 to fix my 15 year old r22 unit before I spent $4000 on a new r410a piece of junk. Best Wishes!! If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
6/29/2017 9:24:02 AM • Goodman... • 137 views • 0 helpful votes
0helpful
1answer

Goodman Model # GMC070-4b

is the thermostat set for heat and you have power going to the unit correct
6/5/2017 8:42:07 AM • Goodman... • 224 views • 0 helpful votes
0helpful
1answer

What is starting sequence?

10/2/2015 1:35:52 PM • Goodman... • 111 views • 0 helpful votes
0helpful
1answer

Goodman gms90703bxa tripping overheat limiters, keeps flashing 6 times, open roolout

When unit come on you need to watch the flames that shooting in all should blue. If there is any red flame kick out that would trip the flame role out switch. If the is the case you need a need heat exchanger.
2/9/2015 4:45:04 PM • Goodman... • 476 views • 0 helpful votes
0helpful
1answer

I have a goodman that flashes 4 times.what do i look for

Sounds like an open limit switch. The limit switch will open due the furnace overheating. Few reasons: 1) Dirty air filter 2) Dirty blower wheel/assembly 3) Weak Capacitor 4) Improper airflow across heat exchanger.
10/6/2014 12:07:58 AM • Goodman... • 840 views • 0 helpful votes
0helpful
1answer

How do I clean my goodman hvac coils and drip pan and where are they?

Coil is separate from furnace. remove screws to door and use a coil cleaner in addition pour some bleach in the drain pan to keep water flowing to outside
6/26/2014 7:18:36 PM • Goodman... • 163 views • 0 helpful votes
0helpful
1answer

Goodman model # AWB2405D

Turn off your power, remover both the upper and lower doors. You may have to disconnect some ''molex' plug connectors and you may have to remove some thermostat wires to gain access. If you remove any wires, WRITE them down as to what terminals they go back on. The molded plugs can only go on one way so don't be too concerned about their replacement UNLESS they are individual plastic plug ins for each wire. If so...WRITE down the location and proceed. There should be either 5/16" or 1/4" headed screws securing the blower assembly in place. The assembly itself is probably slid into position on sheet metal rails or into slots. When the proper two (usually) screws are removed, it will merely slide out the front of the furnace. Place it on the ground and look into the side of the assembly OPPOSITE of the motor. In there you will find a 5/16" square headed set screw. Remove that screw because it secures the blower wheel to the blower motor shaft. Clean rust, dirt and debris off the exposed shaft because that will inhibit the sliding of the shaft OUT of the wheels hub. Turn it over to the motor side up. There will be three bolts or scews securing the blower motor to the blower housing by means of a three legged 'spyder' mount. Remove them and work the motor and shaft OUT OF the blower wheel hub. You are now home free... the motor is removed. Reinstall in basically reverse of the removal procedure. Hopefully you have an IDENTICAL replacement, so there will be no wiring adaptions to figure out.
5/16/2014 7:16:48 PM • Goodman... • 219 views • 0 helpful votes
0helpful
1answer

I bought a freeview+digital tv recorder

www.goodmans.co.uk/support
6/11/2014 5:52:01 PM • Goodman... • 79 views • 0 helpful votes
0helpful
1answer

Furnes 5code weather king

Check bottom door for error codes
7/1/2014 12:45:37 AM • Goodman... • 44 views • 0 helpful votes
0helpful
1answer

How do I get my heater to blow hot air?

I assume this is gas . induced draft blower or ignitor.
4/30/2014 2:50:51 AM • Goodman... • 207 views • 0 helpful votes
0helpful
1answer

Light flashes 4 times

ignition failure. insure air pressure switch closes, hot surface igniter is getting 120volts. check continuity on hot surface igniter, make sure all gas shut off valves are open and gas valve is turned on. make sure there is no blockage in the exhaust
4/18/2014 1:24:28 AM • Goodman... • 190 views • 0 helpful votes
0helpful
1answer

What causes a horizontal ac not to drain

The condenser drain line is clogged.
6/19/2014 7:03:58 AM • Goodman... • 39 views • 0 helpful votes
0helpful
1answer

Flame is high on left back tube of Burner Assembly

The burners need to be removed, cleaned and inspected. Any obstructions on the burners need to be thoroughly cleaned with a wire brush. changing burners to different compartment and still having the same problem in the original chamber, could be a defective heat exchanger.
5/19/2014 9:46:09 PM • Goodman... • 67 views • 0 helpful votes
Not finding what you are looking for?
Goodman GMS90703BXA Heater Logo

1,187 questions posted

Ask a Question

Usually answered in minutes!

Top Goodman Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

Mike Cairns
Mike Cairns

Level 3 Expert

3054 Answers

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers

Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

View Most Popular

Goodman Heating & Cooling

  • Goodman Heating & Cooling

Most Popular Question

goodman furnace gmpn080 4 getting 4 red

  • Heating & Cooling
Loading...