Goodman GMP100-3 igniter will not ignite

Hello, verify if the igniter is receiving a 120 volts from the control board after the pressure switch closes. Sometimes a faulty control board can cause this problem if the igniter and pressure switch are good.
11/5/2012 1:01:12 AM • Goodman... • Answered on Nov 05, 2012
0helpful
1answer

Goodman heating system -gmt1155b is not providing enough heat.

if you are using a single stage with just a W connection not a W1 and W2 then it may be wired to the W1 connection on the furnace contro board. in that case it will only run in first stage. the easiest thing you can do is run a small piece of wire between W1 and W2 on the furnace control board. if you dont have a W1 and W2 connection on the board then its not 2stage, if you have an extra wire at the stat you can get a 2stage stat and wire W1 and W2 individually.
11/1/2012 2:25:45 AM • Goodman... • Answered on Nov 01, 2012
0helpful
1answer
0helpful
1answer

Blower motor

400-500
10/31/2012 10:46:40 AM • Goodman... • Answered on Oct 31, 2012
0helpful
3answers

Goodman GMS90703BXA Heater/AC - 3 Amps Fuse blows

This fuse is used on the low voltage side of the furnace. All 24 volt controls operate thru it. You may have a short in your thermostst, thermostat wire or even a bad transformer. After replacing the fuse, inspect the wiring in the cabinet as well as the wire heading toward the thermostat for damage. If you find none, check the thermostat for loose wires or contacts. If all else fails, jump out R and W with a small jumper temporarly at the furnace and see if the unit runs. You will have to tape the door switch closed to run it with the panel off. Remember, this will keep the furnace running 100% of the time until you disconnect the jumpers. Not a solution, just a test! If it runs flawless, you have a bad thermostat or wire. Diagnosing a transformer is for a technician.
10/28/2012 9:45:37 AM • Goodman... • Answered on Oct 28, 2012
0helpful
1answer

Tempstar pilot turns off

Based on your model number this furnace does not have a pilot light,instead it uses a hot surface igniter.typically it glows and when it gets hot enough the gas valve will open and the burners will light.When the igniter starts to go bad it will glow but not get hot enough to open the gas valve.If your furnace lights and the quickly goes out the flame sensor maybe dirty.
10/10/2012 10:26:22 PM • Goodman... • Answered on Oct 10, 2012
0helpful
2answers

I have a york diamond 90 diagnostic 1 flash lock

open the top of your unit so that you can see into the burner box
what your looking for should be an orange wire that leeads up to a metal rod
that metal rod should be in the way of the flame when unit is on
this is your flame ground,,, or more commonly known as the flame sensor,,, take this out and goive it a good brush with some steel wool
and reassemble,,
this should clear up you problem
10/8/2012 9:48:03 PM • Goodman... • Answered on Oct 08, 2012
0helpful
1answer

Furnace will not start. GMP075-3 Goodman

3 blinks is the pressure switch not working i take it you have a reg on the line from the tank ?
10/6/2012 9:19:10 PM • Goodman... • Answered on Oct 06, 2012
0helpful
1answer

My brand new furance will not stay lite for more than a second

Call back who ever fitted it , they is a years guarantee on it .
9/29/2012 3:05:34 AM • Goodman... • Answered on Sep 29, 2012
0helpful
1answer

Goodman GMH 95, No heat, draft inducer doesn't start. light blinks 3 indicating pressure switch, something I am missing?

If pressure switch does not prove fan does not start on some models
9/20/2012 2:34:28 AM • Goodman... • Answered on Sep 20, 2012
0helpful
1answer

I HAVE A 1999 GOODMAN GMT070-3B FURNACE I PURCHASED USED MUST CONVERT TO PROPANE ,BUT I CANNOT FIND ORIFICE LOCATION

it will be in the combustion chamber on the burner bar you will have to remove the burner to get to it .
9/7/2012 2:29:55 AM • Goodman... • Answered on Sep 07, 2012
0helpful
1answer

How are the wires installed for the AC

Hello, you need to run 18 gauge thermostat wire from the Y and C terminals on the control board to each low voltage terminal on the outdoor contactor side terminals. Best way is th run it along the suction line and support it with wire ties. The high voltage wires will run from the disconnect box on the outside to the high voltage terminals on the contactor coil. The high voltage wires will be run in liquid tight conduit.
8/4/2012 7:48:45 PM • Goodman... • Answered on Aug 04, 2012
0helpful
2answers

Problems with Goodman heat pump.

it's powerd by a relay and only comes on ondemand.
7/31/2012 4:28:01 AM • Goodman... • Answered on Jul 31, 2012
0helpful
2answers

GOODMAN JANITROL GMT070 FUSE

you must see the schematic diagram, and see what amp, and voltage is.If you have doub get customer support from Goodman.comGod bless you
7/10/2012 10:41:10 PM • Goodman... • Answered on Jul 10, 2012
0answers
0answers

Filter size

Be the first to answer 7/2/2012 5:10:56 PM • Goodman... • Posted on Jul 02, 2012Be the first to answer
Not finding what you are looking for?
Goodman GMS90703BXA Heater Logo

1,187 questions posted

Ask a Question

Usually answered in minutes!

Top Goodman Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

Mike Cairns
Mike Cairns

Level 3 Expert

3054 Answers

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers