20 Most Recent
Cross Furnace Draft Inducer Blower 115 Volts Fasco # A064 Questions & Answers
Turned blower fan on to vent the home. Sudenly it
Sunbinder...you will need to do a little troubleshooting. Turn it off again and wait 20 minutes then back on. If no noise or odor. Are you certain that the smell came from the blower. "Thru-out the house is a lot of smell.
Listen closely on startup and running....any unusual sounds. ? Which fan are you talking about ? Furnace ? Vent like bath or kitchen ? If you are handy you can check the wiring connections to be sure they are secure and making good contact with tight wirenuts or screws etc.
16 yr old heil furnace sometime lights on 1st
The air intake may need to be adjusted or check the gas valve or if it is oil check your cad cell it may not be registering your flame and needs to be replaced that is normally pretty cheap. good luck
How to install ge capacitor 27l566
one wire to pin 1 other wire to pin 2 and capacitor
other connection of capacitor goes to pin3
only if we are talking about run capacitor not for startcapacitor.
Heil 75kbtu gas furnace 80% efficiency installed
if it has a pilot, you can follow the pilot tube from the gas valve back to the burner assembly and find it. It may not have one and if this is the case, the air flow switch is supposed to close when the inducer fan comes on . If the flue is clogged, condensation in the bottom of inducer fan(would hear cracking). then after the draft safety switch is closed,the gas vavle will get 24 volts and allow the gas valve to open
My heater no call for heat
this motor is a light duty motor and before it comes on, all of the safety switches...i.e. rollout switches, high limit switch must be closed before voltage will go to the inducer fan will be energized. You can check the fan with an ohm meter and see if you have any resistance. if you do, its good. the door switch on your furnace must also be closed before the furnace will be energized at all
My furnace wont come out of lock out mode
Pressure swithc stuck closed? try undoing on of the wire going to the pressure switch and see if it stays on longer. Make sure you tested all limit switches there are usually at least 3 and up to 5
I would like to find a owners manual
hacve oyu tried Fasco Industriess yet. Yoru blower shouuld had 4 wire on it and come on imediately with a call for heat. the second set of wires are basically a saafe3ty that closes when the unit is spinning they close telling the board or contrller that the fans running. Good Luck and Hope this helps if notthen you can contact me here if ypou care to.
Furnace burner ignites then goes out
Sound like a thermocouple, or flame sensor.
If it has flame sensor make sure you check micro amps to verify operation, because it might be the board that controls the sensor.