Top 20 Leviton 8599 GFCI Receptacle Questions & Answers

Tip

GFCI wont RESET


unplug everyting that's plugged in to all the outlets on that circuit (which that GFCI controls), and then press the RESET button. It should work.

If NOT, unplug it all as above, and then disconnect each receptacle. (be careful that no power is being sent to any of them and that noone touches the wires because it will start working after this). then reconnect the GFCI receptacle only and see if you can press the RESET button then. if so, then you know one of the outlets on that circuit has an issue. connect them each one by one and test if you can reset after each one. If you can, then you know which receptacle it is. try reconnecting that one again,there's a good chance it will work as you have just tightened the wires. if not, then you have a more serious problem, possibly a short somewhere in the wall.

i'm not an electrician, but i just had this problem and this tip was passed on to me by a friend and it worked.

on Jun 17, 2016 | Leviton 8599 GFCI Receptacle


It senses if power is grounding out and interrupts the circuit quickly in order to stop electrocution

Leviton 8599... | 81 views | 0 helpful votes


If there is a ground wire there and it is attached it should read correct. It may also indicate that there is a loose or missing ground wire somewhere else in the circuit.

Leviton 8599... | 92 views | 0 helpful votes


You've lost a neutral connection at: one of the terminals somewhere; inside the outlet; broken strap between the neutral pads on the standard outlet; or the tester is providing an erroneous indication.

Does it read OK on the BOTH receptacles of the first outlet? Check the terminals that provide output on the first outlet and the LINE terminals of the GFCI . Bad at the first outlet? Check the input on the first outlet. Bad? Check splices between outlet and service panel and neutral connection at neutral bus bar inside panel. OK? Check the input to the GFCI - make sure on LINE terminals and proper polarity is observed.

Double check the line and load terminal screws of the GFCI outlet. Make sure that the power coming into the GFCI is connected to the LINE terminals. Be sure to connect the HOT and NEUTRAL wires to the proper LINE terminals. Neutral conductor (white) connects to the silver colored screws and hot (black or red) connects to the gold colored LINE screws. If you are sending power out to supply additional loads that are to be GFCI protected, the rules above apply - but connect to the LOAD screws.

Leviton 8599... | 147 views | 0 helpful votes


GFCI is designed to detect ground faults, and will not reset if ground fault is detected, or if device is bad.
Seems odd that both GFCIs will not reset unless both are outside.
If GFCI is outside, they get dirty and wet, and the GFCI goes bad.

If GFCI will not reset, open following links:
http://waterheatertimer.org/pdf/GFCI-outlet-will-not-reset.pdf
http://waterheatertimer.org/How-to-wire-GFCI.html

Leviton 8599... | 511 views | 0 helpful votes


Has indicator always been ON?
Or did it suddenly turn ON recently?

Usually small indicator lights show that device is working, and has power.
Then when GFCI trips, the light goes off.

Add a comment for more free help.
Also take advantage of fixya expert assistance live.
For a price, expert works with you via e-mail or phone while you work on circuit or any do-it-yourself project.
Fixya is always less expensive than a service call.

Leviton 8599... | 1,441 views | 0 helpful votes


There's a short or ground fault somewhere in the switch, wire or light fixture.
Process of elimination can locate problem.
Replace the switch, and check circuit.
Disconnect wires from florescent and connect trouble-light pigtail, and check circuit.
Replace light fixture.

Upvote the help.
And take advantage of fixya expert assistance live.
For a price, expert works with you while you work on circuit or any do-it-yourself project.
Fixya is always less expensive than a service call.

Leviton 8599... | 73 views | 0 helpful votes


If you can find a higher rated GFCI receptacle it may help. But the first thing is to use 12 ga wire (NOT 14), and to get a good and tight connection to the load lug. Use the screw terminal, not the push-in holes. If you can remove the screw, do so. Then shape the end of the wire into a nice hook and then use a hammer and anvil to flatten it slightly. Then insert the screw nice and tight. If you can manage a 10ga wire, use that.

Leviton 8599... | 359 views | 1 helpful votes


You first install the adaptor then "snap" the screwless cover to the adaptor. See link to leviton web site: http://www.leviton.com/OA_HTML/ibcGetAttachment.jsp?cItemId=2gfWNEOgKddmIKzlZrTgaw&label=IBE&appName=IBE&minisite=10026

Leviton 8599... | 214 views | 1 helpful votes


Either the GFI is bad or it is tripping because there is a short in the system (obviously, right). I would turn off your panel break, disconnect the GFI and using a meter test to see if there is a short in the system. You would check the hot lead coming from the GFI to the tub and see if it is shorting. If you can't find a short, you should try replacing the GFI. If there is a short then you need to search for the short. Hope this helps and good luck!

Leviton 8599... | 1,450 views | 1 helpful votes


Only heats the water.

If you need to cool it drain 20% of the water and replace.

Hope this helps

Leviton 8599... | 39 views | 1 helpful votes


Hello
No ! not recommended,you need a dedicated circuit for each bathroom.

Since you will be using ground fault protection or a gfi circuit.

You can use 2 or 3 gfi in one bathroom but they must be connected to one breaker.

Thanks and have a good day.

Leviton 8599... | 66 views | 0 helpful votes


They put the GFI in line at the front, all the other plugs run off it. One of the other plugs, has lost ground, has lost neutral, a simple plug in tester will tell you this, find the fault, or,, you have a fluorescent bulb plugged into it. The gfi's are very sensitive, they snap at the drop of the barometer.

Leviton 8599... | 148 views | 1 helpful votes


if its like the outlet in the picture try hitting the reset on the outlet

Leviton 8599... | 70 views | 0 helpful votes


This has to be the gfi, They are designed to kick out at the slightest hint of of a short or power to ground. I personally have had a few bad experiences with the 15 amp GFI recepticles, and have upgraded to an industrial style 20 amp model which is still acceptable for code here. Check your local electrical codes before doing this, and make sure it is the first recepticle in the circuit.

Leviton 8599... | 236 views | 1 helpful votes


typically, the transformer fails. As bulbs become older, the power to run them goes way up, overloading the transformer....

Leviton 8599... | 1,064 views | 1 helpful votes


is there another light in the vacinity or is the light in question itself pointed at the photocell. most likely scenarios are that the light is pointing at its own photocell so when it is off the photosell senses dark and turns it on but then when light comes on tricks photocell into thinking it is daylight,check position of photocell and adjust away from light source if problem persist could be ballast going bad

Leviton 8599... | 372 views | 0 helpful votes


how old is it ? GFI's internal parts wear out,can't be fixed.all three receptacles are being protected by the one w/GFI

Leviton 8599... | 168 views | 0 helpful votes

Not finding what you are looking for?
Leviton 8599 GFCI Receptacle Logo

Popular Tags

27 questions posted

Ask a Question

Usually answered in minutes!

Top Leviton Electrical Supplies Experts

jdthefixer

Level 3 Expert

746 Answers

Gene Haynes

Level 3 Expert

5353 Answers

boomanfoo

Level 1 Expert

23 Answers

Are you a Leviton Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

View Most Popular

Leviton Electrical Supplies

  • Leviton Electrical Supplies

Most Popular Question

gfci oulet triping only thing circuit

  • Electrical Supplies
Loading...