20 Most Recent Kohler 100-Amp Automatic Transfer Switch - RDT-CFNA-0100A Questions & Answers
The problem is not likely battery related. It sounds like either an ignition or fuel control relay that is not actuating due to missing electrical voltage.
Kohler 100-Amp... | Answered on Nov 26, 2017
http://www.kohlerpower.com/onlinecatalog/salesservicelocator.htm
Kohler 100-Amp... | Answered on Feb 17, 2013
sounds like the voltage sensor is either mis adjusted or burnt up. Also could be a wire disconnected on the voltage sensor board.
Kohler 100-Amp... | Answered on Mar 11, 2010
Six steps of start-up Shangchai generator set :
A.Unscrew the deflation screw on the fuel injection pump, use the fuel hand pump to remove the air in the fuel system, and fix the adjusting control handle on the throttle position of the suitable starting speed;
B.Pressthe generatorstart button to start the diesel engine. If the diesel engine can't start in 10 seconds (up to 15 seconds), it should wait for 1 minute before starting for the second time. If it can't start for three consecutive times, should check and find out the cause of the failure;
C.After diesel generator set start up, the no-load speed gradually increases to 1000-1200 r/min (note not to run at low speed for a long time). After the diesel engine is preheated, the speed is increased to the rated speed. When the outlet water temperature reaches 55 degrees Celsius and the oil temperature reaches 45 degrees Celsius, full load operation is allowed;
D.After starting the diesel engine, pay close attention to the reading of oil pressure gauge (2.5-3.5kg/C?in normal operation). If the oil pressure gauge does not indicate, stop immediately and check whether the ammeter has charge indication;
E.After the diesel generator set is put into normal operation, should observe the changes of water temperature, oil temperature and oil pressure at any time, and should handle the reading of power meter, frequency meter, ammeter and voltmeter in time if abnormalities are found;
F.When each instrument of the genset indicates normally, can turn on the load switch to send power to the load. With the change of load of the genset, if the frequency and voltage are not within the prescribed range, should adjust the frequency and voltage in time to maintain the rated value. It is strictly prohibited that the genset carry load at low speed, so as to avoid damage to the equipment.
Kohler... | Answered on Sep 30, 2019
contact the maker,
ask them,
or buy one off ebay, using facts above
there is no other way. (there is a parts list at most makers web sites,Valsi
omg first google hit.
http://www.valsi.com.mx/
Kohler... | Answered on Sep 17, 2019
Maybe you can contact the supplier who provide the generator for you. Or you can read manual operation of use.
In the future, if you plan to have a diesel generator set, welcome to contact us: https://www.dieselgeneratortech.com/generator-set/
Kohler... | Answered on Aug 31, 2019
Can you be more specific? what model Kohler is it, Model number KW etc.
Kohler... | Answered on Aug 30, 2019
I think you can ask your supplier, they most know their generator.
If you plan to have a new diesel generator set, maybe you can consider Cummins, Volvo, Perkins, as well as China made generator: Yuchai, Shangchai, Weichai, Ricardo etc.
Here is the website:
https://starlightgenerator.en.made-in-china.com/
Kohler... | Answered on Aug 23, 2019
Request the diagrams from Kohler and compare.
Kohler... | Answered on Aug 21, 2019
The engine is failing to run after a commanded start. Repeatedly.
Kohler... | Answered on Apr 19, 2019
Are there any faults listed on the control display? If display is dark then likely a battery issue. Check battery voltage with a Digital Multi Meter (DMM). It should be at least 12.5VDC.
Kohler... | Answered on Apr 17, 2019
Sounds Like possibly the regulator is the issue.
Flightsystems Can test these to see if it is good or not.
also here is a link for the service manual
https://us.v-cdn.net/5020499/uploads/editor/0c/g1lx13xi2vyy.pdf
Kohler... | Answered on Apr 16, 2019
the parts manual is a tp-5317 which I do not have . You said its a dec2? or a fast response 2? What is the part number off the main circuit board in the control box?
if you have an scr pack, that has 6 pins, there are two for ac, two for gates, and two for the excitation field.
The two gate wires come off your adc controller.
http://www.kohlerpower.com/onlinecatalog/pdf/g2058.pdf
Safety shutdowns:
  1. Loss of coolant
  2. High water temperature
  3. Low oil pressure
Likely one of these. If no indicators at a panel check at the connector.
Kohler... | Answered on Feb 19, 2019
Kohler 100-Amp Automatic Transfer Switch - RDT-CFNA-0100A Logo
5 questions posted
Top Kohler Electrical Supplies Experts
Sheldon Dedek
rjivaro
J. Bradshaw
Are you a Kohler Electrical Supply Expert? Answer questions, earn points and help others
View Most Popular
  • Kohler Electrical Supplies
Most Popular Question
when weekly scheduled start
  • Electrical Supplies
