I have a 13kw lp

This sounds like the stepper motor is failing with heat. Given the Hz signal is straight from the alternator.... a loss of the signal would intially cause the unit to overspeed. (Wiring from alternator to control board problem maybe... also heat related)
The only thing that made sense to me is a problem in the 10 Ohm freq sensors or the stepper motor.

Noting you have changed the control board and your still having overspeeds Look at the the Hz sense portion. I would bet your shutdonws are being initiated due to over-voltage vs over-speed. That you may have to sort out.

Sounds like a long day... of troubleshooting. 5 - 6 hours wait and then PANIC just to duplicate it!
Hopefully you have the service manual. I have the one for the 15Kw and Up.. but sense circuitry is pretty much the same.

Sense circuit...

* Measure resistance across any combination of orange, yellow, brown, or black should read approximately 20 OHMS.

* Measure from red to any other lead should read 10 OHMS.
* Testing from any lead to stepper motor case should read INFINITY.

Orange or black to Black or green One leg... 20 Ohms
Yellow or Red to Brown or white 2nd leg 20 Ohms

Again Stepper motor or sense wiring / windings... is where I think the problem lies.

Good luck and I am willing to keep taking stabs at this. 40 years as an electrican here.
Thanks for choosing FixYa,
Kelly

9/1/2011 1:32:32 AM • Generac Guardian... • 126 views • 0 helpful votes
0helpful
1answer

My Generac Guardian 15,000 Watt Model 004582

Hi Jake and welcome to FixYa. I am Kelly. Check both CB1 and CB 2 circuit breakers by pushing them to OFF and then back ON. Open the brush block access and then start the unit. You should read voltage at the brushes of 5 - 14 VDC on the terminals of the brushes. If you do not have 5 - 14 VDC at the brushes the probable suspect is the automatic voltage regulator (AVR). If you do have the correct voltages then with the unit OFF.... do a resistance check across the armature coil by reading resistance at the brush block terminals. You should read around 180 Ohms. It can be more or less resistance but for sure less than 500 Ohms. If you do NOT get a resistance reading remove the brush block assy and test the armature directly by reading across BOTH slip rings. You should get the resistance previously stated. If you have resistance then most likely there is a problem with the brushes. (Too short / broken carbon brush / missing spring or a defective terminal.) Without knowing the AVR output voltage and the armature resistance reading at this point it is difficult as to how to advise you to proceed. Let me know the values you obtain for AVR DC voltage at the brushes and actual ARMATURE resistance reading. Make sure you use R x 1000 on the meter. I am having thoughts of maybe a broken wire somewhere inside the control panel also.

Thanks for choosing FixYa,
Kelly
1/9/2011 3:18:44 AM • Generac Guardian... • 2,549 views • 0 helpful votes
0helpful
1answer

My 15kw portable model 004582

Sounds like you missed the low speed jets when you cleaned the carb. They are very small holes and sometimes are behind a plug either rubber or brass.
2/3/2011 12:45:03 AM • Generac Guardian... • 319 views • 0 helpful votes
4helpful
2answers

I have a Generac 15KW generator, the starter went

I suspect you will SOMEPLACE find protection fuse(s) for the sense lines from the utility. That is the first place to check.
3/22/2010 11:11:19 PM • Generac Guardian... • 681 views • 4 helpful votes
0helpful
1answer

Small 7kw Generac has always sounded rough over

If the generator is out of warranty, you can try spraying a short shot of ether into the intake of the generator as it is running rough. If the engine smoothes out for a few seconds, and returns back to original state, then it is likely running lean. Check the gas regulator (this is LP or natural gas I am assuming since it is standby), the vent may be clogged on the bottom of it.
2/11/2010 7:57:09 PM • Generac Guardian... • 810 views • 0 helpful votes
0helpful
1answer

Thinking of buying 5522. Want to hook up to Trace

You need to contact TRACE about this endeavor. The inverter will have to work with the generator's control, likely in manual mode. An adapter may be needed for the inverter to allow it to create the signals that the generator expects.
2/3/2010 11:03:14 PM • Generac Guardian... • 130 views • 0 helpful votes
0helpful
1answer

Had a power interruption last

How is the battery condition? The click you hear is the starter solenoid pulling in. Check all the connections at the battery, engine ground and starter including the solenoid. You have to 'load test' the battery. Just reading the voltage on the terminals isn't good enough, a near dead battery will read 12 volts with 'no load' If you need further help, I’m available over the phone at https://www.6ya.com/expert/craig_3fa289bf857b1a3c
7/12/2009 4:07:36 PM • Generac Guardian... • 229 views • 0 helpful votes
3helpful
1answer

Water in oil

Natural gas and Propane engines do create moisture in the engine because these are cold gases. Therefore, when the engine is done running, the engine is hot and whatever gas is left will condensate and the moisture will drop to the bottom of the engine or oil pan. If this is using these gases then it is normal what you are seeing.
5/2/2009 12:30:47 AM • Generac Guardian... • 371 views • 3 helpful votes
0helpful
1answer

DOES ANYONE KNOW ALLGENERATOR WINDING RESISTANCES ?

5 Ohms at the rotor.
Disconnect all the stator wires and measure each one to ground, it should read opened.
Before disconnecting wires, mark which are hot and which are neutral. Measure between the hot neutral wires and some should read at least 0.5 ohms. You should have T1 and T2 reading 0.5 and T3 and T4 reading 0.5. T1 and T3 should read opened, T1 to T4 should read opened. Also, T2 to T3 should be opened and T2 to T4 opened.
4/12/2009 1:22:57 PM • Generac Guardian... • 229 views • 0 helpful votes
0helpful
1answer

Generac Guardian 15kW Generator

That sounds just about right, if the relay contacts get welded together it sometimes takes out the driver on the printed circuit board. As you found out, 12vdc from 23 to 194 makes the transfer switch move to the Generator position, relay not energized makes the ATS move to the Normal position.

You can make a nice test function by installing a 10 amp contact switch in series with either the N1 or N2 terminals. When the switch is open the generator thinks the Normal power has failed.

Regards,
Carl
1/20/2009 3:02:11 AM • Generac Guardian... • 1,574 views • 0 helpful votes
0helpful
2answers

Transfer switch will not switch back to utility

its the problem of the switch and it has to be replace in such cases to make it proper.it is necessary to replace the switch.
12/25/2008 8:01:32 PM • Generac Guardian... • 312 views • 0 helpful votes
0helpful
1answer

Where can I get fuel pump for Generac generator model 09856-0 5000watt

Generac should be able to advise; https://generac.ordertree.com/
2/3/2024 6:52:10 AM • Generac... • 22 views • 0 helpful votes
0helpful
1answer

Generac 389cc Generator. How to set the timing on the generator please?

Question edited for clarity, spelling (timeing) and toss in some CAPS. Engine timing and Valve timing in the link. https://www.google.com/search?q=Generac+389cc+Generator.+How+to+set+timing You could also search for a Service Manual, but you will need the model number rather than the cubic capacity of the engine cylinder. ..
11/29/2023 3:32:02 PM • Generac... • 36 views • 0 helpful votes
0helpful
1answer

Generac Standby Generator. I have a red blinking light on on the OFF button on the Guardian 2.0 control panel?

Question edited for a lot more clarity. Model and KVA helps. Question moved from Televisions to Generac Guardian category. Information to troubleshoot in the link and video. https://www.google.com/search?q=generac+guardian+standby+generator+switch+off+led+flashing+red ..
9/20/2023 4:50:42 PM • Generac... • 53 views • 0 helpful votes
0helpful
1answer

Generac won't turn off unless I pull the fuse.

James, Which unit are you dealing with 12k 15k 17k 20k 22k 24k? You have a ats. automatic transfer switch?
6/26/2023 10:56:22 PM • Generac... • 55 views • 0 helpful votes
0helpful
1answer

Generac 0058711, 10KW Generator. How to reflash home standby 10kW Generac generator model number 0058711 please.

That is a full home back-up unit. You need dealer support. Contact them direct. There is nothing online about re-flashing.

Support For Your 0058711

Generac Power Systems https://www.generac.com > product-support-details File Type Manual (PDF) Item Number Langu... Emissions Warranty Statement WARRANTY STATEMENT EMSN E P3 0J3335 EN Exploded View (Control Panel) EV CONTROL PANEL ? HSB 0J3707 EN Exploded View (Enclosure) EV ENCLOSURE HSB 2011 0J4730 EN View 29 more rows
6/11/2023 1:23:12 PM • Generac... • 51 views • 0 helpful votes
Not finding what you are looking for?
Generac Guardian 100 Amp Transfer Switch with Service Disconnect NEMA 3R Logo

18 questions posted

Ask a Question

Usually answered in minutes!

Top Generac Electrical Supplies Experts

vince

Level 3 Expert

2530 Answers

Brad Brown

Level 3 Expert

19187 Answers

Paul Bade

Level 3 Expert

1818 Answers

Are you a Generac Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

View Most Popular

Generac Electrical Supplies

  • Generac Electrical Supplies

Most Popular Question

generac 15kw generator starter went

  • Electrical Supplies
Loading...