relay in your transfer switch is staying energized when we don't want it to be. On the terminal board inside the transfer switch you should see terminals labeled 194 and 23, these are the power to the
...transfer relay thru wire 194 then back to terminal 23. This is held open till the startup timer times out and only after the warmup does wire 23 close to ground. This energizes the transfer relay, ...
Question about Generac Electrical Supplies
...relay. contact generac,sometimes they will accomodate you with new parts My 200 Amp transfer switch just burned up the upper coil for the 3rd time in about 2.5 years. Each time it occurred when the ...
Question about Generac Electrical Supplies
...transfer if you do not show 12VDC. Then you have a relay hanging upon the PCB board in the generator, need to replace board. If you are showing 12VDC and the switch is not transferring the problem is ...
Question about Generac Electrical Supplies
transfer to the generator. Any ideas? Check the connections on the tranfer relay and two coils. The two coils have blue wires. I have seen them come off from assembly or shipping its common. Each coil
...transfer switch move to the Generator position, relay not energized makes the ATS move to the Normal position. You can make a nice test function by installing a 10 amp contact switch in series with ...
Question about Watts Electrical Supplies
...transfer switch, did now says error fault relay switch. Parallax ats501 why now there is a error fault? Could something else be causing this problem? Check to see if you have power going into the ...
Question about Electrical Supplies
I have a new 20 kw propane gen. Eaton generac, with a generac transfer switch/load center combo.When I simulate a power outage the gen starts up transfer switch changes states, power is on all workin ...
Question about Generac Guardian Electrical Supplies
...transfer switch, if you have battery voltage(12-13.5 VDC) then you you probably have a stuck relay on the PC board in the generator. The board needs to be replaced. If you don't have battery voltage ...
Question about Generac Electrical Supplies
automatic transfer switch not transfering power to home upon loss of city power the generator starts and runs but no power reaches home YOU MAY WANT TO CHECK THE RELAYS THAT ARE IN THE TRANSFER BOX
35 questions posted
Usually answered in minutes!
58 Questions
2 Questions