I have a 6000 watt allpower generator that the 12 volt breaker poped out reset it still no power replaced the avr ran for about 5 seconds then poped the 12 volt breaker again what could it be

2 Answers

Generator Guru Parts

Level 3:

An expert who has achieved level 3 by getting 1000 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Master:

An expert who has achieved Level 3.

  • Master 286 Answers
  • Posted on Dec 06, 2016
 Generator Guru Parts
Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Master:

An expert who has achieved Level 3.

Joined: Nov 12, 2010
Answers
286
Questions
1
Helped
148847
Points
1274

Barry,

The 12v system does not go through the AVR. It most likely is the Battery Charging Rectifier has failed. This controls the voltage from the 12v feed from the alternator and charges the battery.

1) Follow the wiring from the 12v socket/connectors until you come to a Block rectifier. It will be held on by a bolt in the center and have 4 wires connected to it. If you look at the pins you will see one is seated at a different angle to the others. Test the feed to this pin, you should get a result of between 12 Volts DC to 16 Volt DC.
If you are not getting these results then the Block rectifier has blown and will need replacing. http://www.generatorguru.com/rectifier-98406168/

2) If all is testing fine above, then you will need to test the Battery Charging Rectifier as you have an Electric Start and Battery on your unit. This is a metal block located on the back of the engine, next to the starter motor and it has fins running across it. ( to see an example of this part look up your generator on this page http://www.generatorguru.com/all-power/) Again this should be giving you between 12 Volts DC to 16 Volt DC.

3) Next,check the voltage going into the Battery Charging Rectifier from the alternator. You should get between 12 Volts DC to 16 Volt DC.

For replacement parts please see our web page. You will need the full model number to do this.:

http://www.generatorguru.com/all-power

  • Barry Bordeau
    Barry Bordeau Dec 07, 2016

    Hi thanks for the info. but it does not have a starter or a bridge rectifier it as 3 plugs coming from the stator one to the avr the 2 in to the panel i disconnected the 2 gray wire plug and the 120 volt works but not the 12 volt could it be the 12 volt breaker gone bad

  •  Generator Guru Parts

    Would you like to call our engineers? We have a number of engineers who have worked a number of times on these units. When you call ask for the "All Power America" specialist. :)http://www.generatorguru.com/ask-the-gur...

×

Lawrence Oravetz

Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

  • Allpower Master 10,558 Answers
  • Posted on Dec 06, 2016
Lawrence Oravetz
Allpower Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Joined: Jul 28, 2008
Answers
10558
Questions
1
Helped
2699769
Points
29284

What 12volt load do you have connected to the 12volt connector? You may be overloading the circuit.

Testimonial: "No 12 volt or 120 at all soon as i start it it pops"

  • 1 more comment 
  • Lawrence Oravetz Dec 06, 2016

    Ahh, OK. The diode rectifier is most likely shorted internally.

  • Barry Bordeau
    Barry Bordeau Dec 07, 2016

    thanks for the info but it does not have a bridge rectifier i unplug the 12 volt widings and the 120 volts work don't no were to go from here

  • Barry Bordeau
    Barry Bordeau Dec 29, 2016

    you were right the rectifier was in the eletrical panel and not on the generator head

×

Ad

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

Craftsman 5600 watt generator AVR Location? It does not appear to be inside the cover of alternator.

The most common cause of portable generators failing to produce electricity is from the loss of residual magnetism.

Generators work by moving electrical conductors through a magnetic field. Your generator does not have magnets. The magnetic field is created by taking some of the generator output voltage and converting it to DC and feeding it to a coil to make an electromagnet.

When there is a small amount of magnetism left over from the last time the generator was running, it is called residual magnetism. The little bit of magnetism is enough to produce a small amount of electricity. This small amount of electricity is needed to create an even stronger electric magnet. As the engine turns this magnet moving its electric field, through the stator windings, your generator produces even more power.

When the residual magnetism is lost, the generator will produce no power at start-up. This residual magnetism can be lost naturally from not being used or from the load on your generator being connected when the generator is shut off. It can also happen from running a generator with no load for too long.

Generators need to work and it helps maintain that residual magnetism. When they are running, a load should be connected to it. It helps create an even stronger magnetic field. Before you shut it off, turn off the switch or breaker to disconnect the load. If you shut off a generator with the load connected, it can essentially drain or demagnetize the electromagnet. Try and avoid running out of fuel.

How to fix it:

There are a few methods of restoring a generator residual magnetism

12 Volt Generator Battery Method

Locate the voltage regulator for your generator.
Unplug the two wires that connect to the generator brushes. Normally one is red and the other is black or white.
Connect the black or white to the generator ground battery terminal.
Plug in a light, turn on the generator breaker or switch and start the motor.
Connect the battery +12 volts (red cable) to the red wire on the terminals you removed for three seconds.
Remove your wires and replace the plug. The generator should now be producing power again.
0helpful
1answer

How many volts is 1200 watts

Watts to volts doesn't translate as they are different units to measure things. Watts is a power measurement while volts is what is trickling through the cable. You could have 12 volts at 6000 watts or 240 volts and 5 watts, depends on usage. If it's for a car audio amp, it will be generally 12 volts to power it which at 1200 watts means it will run at around 100 amps current according to ohmslawcalculator.com
0helpful
1answer

My Multiquip GA6HA generator only puts out 1 volt any ideas for troubleshooting?

Sounds like the alternator has failed, possibly a short or open in the windings. Similar to problem I had with my 10 KW unit. I replaced the alternator.
0helpful
1answer

How many 5 watt outside lights can you power with a 20 amp breaker?

Volts x amps= watts.
20 amp breaker x 125 volts = 2500 watts.
However, electrician use the 80% rule, so multiply 2500 x 80% = 2000 watts.
So if you have 20 amp breaker, and 12 gauge wire, and 20 amp switch, and distance is less than 150 feet, then watt load is 2000 watts or 400 5-watt bulbs.
Keep in mind that most switches are 15 amp, and not 20 amp.
Recalculate for 15 amp switch = 1875 watts x 80% = 1500 watts or 300 5-watt bulbs.

If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7

Jun 22, 2012 • Home
0helpful
1answer

I have a briggs and stratton 8500/5500 generator which I am using to power an air conditioner on a camper trailer. I just recently started having a problem where the one circuit breaker keeps tripping when...

Hello, First figure out what the load per leg is on your generator. Are you using the 240 Volts because this is two 120 AC volts legs and they are 120 degrees out of phase with each other.

You will need to figure what the power factor is for each phase on this generator. To figure the power/wattage by using ohm's law. Voltage times Current will give you Watts. Example: If the generator is generator 240 volts the maximum current available is about 23 amps. The maximum current for 120 volts will 46 amps. Therefore, the maximum current per 120 volt circuit is 23 amps for one circuit and 23 amps for the second 120 circuit..

I would try replacing the circuit breaker with the same amperage breaker. Also, watch what the generator load is per circuit. You can install current meter for each circuit. This will give a good indication of which circuit is pulling more load than the other circuit. GB...stewbison
0helpful
1answer

My generator turns on but, supply's no power?

You must check:
  1. Are your breakers ON?
  2. Measure the voltage on generator terminals.
  3. If the voltage is less than 20 V AC, you should check the excitation field, rings and brushes, AVR - rectifier, cables and fuses.
  4. If every thing is OK you may need to recharge the DC field with a short connection of "+" and "-" of a 12 V battery to respective field terminals when the engine is running.
  5. If the AC voltage raises for a second and drops when you disconnect the battery - the excitation circuit is bad.
2helpful
1answer

High voltage

Great, JP. Could I ask you to please rate my assistance. Thanks very much!

Charlie
0helpful
1answer

Protection light blinks and beeping

it has been through an overload (hence the protection light) and needs its breaker to be reset (look for a poped out button and push it back in) or it needs a new fuse (replace ONLY WITH THE EXACT SAME MODEL OF FUSE or it will either blow too early or too late (or not at all) when there is a surge.
0helpful
4answers

How do i flash my generac 5000 power plus generator

well I have a special flasher unit but I believe you can put 12 volts to the brushes while it's running. That should do it.
1helpful
2answers

No electrical output

probably your AVR card is burnt...
an AVR card is located right outside the stator...looks just like an AK-47 clip (i don't know how else to describe it)...i put a pic below this.
replace it and check again
466fecd.jpgAVR location
168ff0f.jpgAVR card
Not finding what you are looking for?

123 views

Ask a Question

Usually answered in minutes!

Top Allpower Electrical Supplies Experts

Brad Brown

Level 3 Expert

19187 Answers

john h

Level 3 Expert

29494 Answers

ADMIN Andrew
ADMIN Andrew

Level 3 Expert

66949 Answers

Are you an Allpower Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...